F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Ťažká

What is the main difference between a dry evaporator and a flooded evaporator?


A dry evaporator does not require an expansion valve, whereas a flooded one does
A dry evaporator allows the entire refrigerant to evaporate in the pipe upstream of the compressor; in a flooded evaporator, part of the refrigerant remains in a liquid state within the evaporator
A dry evaporator is filled with refrigerant liquid, whilst a flooded evaporator is filled with gas
A dry evaporator has a lower operating pressure than a flooded one

2

Ťažká

What is the typical pressure in deep-freezing systems (below −40 °C) for an evaporator in a system using R717?


A pressure varying between 10 and 20 bar
Atmospheric pressure, approximately 1 bar
Positive pressure, in the range of 5–10 bar
Negative pressure (vacuum), below 0 bar

3

Ťažká

Why are PFAS substances formed as a result of the decomposition of certain F-gases problematic?


They are climate-neutral
They are readily biodegradable, so they only pollute the environment for a short time
They cause rapid cooling of the atmosphere
They are persistent, accumulate in the environment and may be toxic

4

Ťažká

What is the basic requirement when charging a system with R717 (NH₃)?


Charging should take place in a well-ventilated area using appropriate personal protective equipment
NH₃ can be charged together with air
Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment

5

Ťažká

How should oil be handled in systems using R717?


The oil should be checked regularly and any excess removed from the lower parts of the units to prevent reduced heat transfer and leaks
The oil does not require any monitoring
Oil can be mixed with any refrigerant
Oil has no effect on the system’s operation

6

Ťažká

What is the correct procedure for recovering R717 from a system?


The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The gas can be released into the atmosphere
The refrigerant can be drained into the sewer system
Recovery is not required

7

Ťažká

How should R717 (NH₃) be stored?


In sealed, labelled containers, in a cool and well-ventilated place
In unmarked plastic containers
In any open containers
Near heat sources

8

Ťažká

What should be done in the event of R717 contamination?


Continue to use without restriction
Add water to dilute it
The refrigerant must be purified or sent for disposal in accordance with regulations
Release into the atmosphere

9

Ťažká

What is the main hazard associated with an R717 leak during maintenance work?


No risk whatsoever
Toxic to humans and may cause chemical burns
Increased cooling efficiency
Damage to electrical equipment only

10

Ťažká

What action should be taken if an NH₃ leak is detected?


Close your eyes and carry on working
Evacuate personnel immediately and remove the source of the leak, if it is safe to do so
Ignore it and carry on working
Increase the pressure in the system

11

Ťažká

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
Neutralises ammonia through absorption in a liquid (e.g. water)
They store the refrigerant
They increase the pressure in the system

12

Ťažká

How should the system be prepared before filling with R717?


Simply start it up
Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level
There is no need to check it

13

Ťažká

What are the transport requirements for R717?


It can be transported without labelling
It can be transported in open containers
Must be transported in suitable, labelled containers in accordance with ADR regulations
Transport is not subject to regulations

14

Ťažká

What personal protective equipment is required when working with NH₃?


Workwear only
Safety goggles, gloves and respiratory protective equipment
No requirements
Only a safety helmet

15

Ťažká

Which statement best describes the behaviour of R717 and mineral compressor oil?


In an R717 system, a return oil line cannot be used because the oil is too hot
R717 mixes very well with compressor oil and easily returns to the compressor
R717 does not mix with compressor oil, so the oil remains in the system on the high-pressure side as a layer above the R717
R717 does not mix with compressor oil, so the oil remains in the system on the low-pressure side as a layer beneath the R717

16

Ťažká

Which system may require manual oil recovery?


Supercritical ‘booster’ system using R744
An R717 system
Secondary system using R744
R744 cascade system

17

Ťažká

Which refrigerant is lighter than air?


R1234ze
R717
R744
R1270

18

Ťažká

R717 is highly corrosive to


stainless steel
copper
titanium
aluminium

19

Ťažká

What is the effect of repeatedly opening the relief valve?


The relief pressure drops
The valve will not open
The valve remains fully open continuously
The relief pressure rises

20

Ťažká

What is the relationship between the pressure (P) and temperature (T) of nitrogen at the start (1) and end (2) of the leak test?


P2 = (P1 × T1)/T2
P2 = T2/(P1 × T1)
P2 = (P1 × T2)/T1
P2 = T1/(P1 × T2)

21

Ťažká

What is the recommended alarm level for fixed leak detection systems for R717?


50,000 ppm
5,000 ppm
500 ppm
500,000 ppm

22

Ťažká

Why are compressors with a separate electric motor most commonly used in R717 (NH₃) refrigeration systems?


To increase the amount of refrigerant in the system
To reduce the condensing pressure
Because NH₃ reacts with the motor windings and hermetic compressors are not used
Because compressors with a separate motor are cheaper

23

Ťažká

Which type of compressor is most commonly used in large ammonia systems?


Diaphragm compressor
Rotary vane compressor
Hermetic scroll
A reciprocating or screw compressor

24

Ťažká

How is the capacity of a piston compressor regulated in NH₃ systems?


By increasing the condensing pressure
By reducing the refrigerant charge
By unloading the cylinders or changing the rotational speed
Solely by adjusting the oil volume

25

Ťažká

How is the capacity of a screw compressor most commonly controlled?


By using a slide valve
By changing the type of oil
By adjusting the oil level
By closing the suction valve

26

Ťažká

When is two-stage compression used in NH₃ systems?


At very low vapour pressures and high pressure differentials
Exclusively in small systems
At small temperature differences
Only with water-cooled condensers

27

Ťažká

What is the advantage of two-stage compression over single-stage compression?


No need for a separator
Lower efficiency
Higher efficiency and lower discharge temperature
Higher energy consumption

28

Ťažká

How does an evaporative condenser used in NH₃ systems work?


It utilises the evaporation of water to increase cooling efficiency
It does not require a water supply
Operates without a fan
It transfers heat only to the air

29

Ťažká

What is the function of the liquid separator in an NH₃ system?


It separates oil from the refrigerant
It prevents liquid from entering the compressor
Regulates the condensing pressure
Increases the discharge temperature

30

Ťažká

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To reduce the condensing temperature
To maintain the correct refrigerant level and prevent the compressor from flooding
To increase the oil volume

31

Ťažká

What is the role of the float switch in NH₃ systems?


It is used to detect leaks
It regulates the condensation temperature
It monitors the liquid level in the tank or separator
It controls the fan’s operation

32

Ťažká

What is a thermosiphon in NH₃ systems?


An oil circulation system utilising differences in pressure and temperature
A type of safety valve
A defrosting device
A type of evaporator

33

Ťažká

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To increase the amount of refrigerant
To reduce the pressure
Because NH₃ does not mix with most compressor oils
Because the oil mixes only with water

34

Ťažká

What is the main function of an oil separator in NH₃ systems?


To increase fan efficiency
Removing moisture from the system
To separate the oil from the refrigerant and return the oil to the compressor
To lower the condensation temperature

35

Ťažká

Which NH₃ system features direct evaporation of the refrigerant in the evaporator?


Glycol system
Thermosiphon system
Direct expansion (DX) system
Indirect system

36

Ťažká

What is the characteristic feature of a flooded evaporator system?


The evaporator contains a large amount of liquid, which improves heat transfer
No level control is required
No separator is used
The evaporator is filled exclusively with vapour

37

Ťažká

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In a direct system, there is no evaporator