What is the main difference between a dry-expansion and a flooded evaporator?


In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
A dry-expansion evaporator always has a lower pressure than a flooded one

2

Nehéz

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 5–10 bar
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Atmospheric pressure, approx. 1 bar abs
Positive pressure of 10–20 bar

3

Nehéz

How is oil managed in R717 systems?


Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil has no effect on system operation
Oil can be mixed with any refrigerant
Oil requires no monitoring

4

Nehéz

What should be done with contaminated R717?


Continue to use it without restriction
Dilute it with water and reuse it
Release it into the atmosphere
Purify it or send it for disposal in accordance with regulations

5

Nehéz

What should be done if an NH₃ leak is detected?


Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system
Carry on working with the room door open
Carry on working wearing a dust mask

6

Nehéz

What role do scrubbers play in NH₃ systems?


They increase the pressure in the system
Neutralise ammonia through absorption in a liquid (e.g. water)
They store the refrigerant
They are used to measure temperature

7

Nehéz

How should the system be prepared before filling with R717?


Simply start it up
The pressure must be increased above the standard level
Check for leaks, remove air and moisture, and create a vacuum
There is no need to check it

8

Nehéz

What are the transport requirements for R717?


It can be carried in open containers
Transport is not regulated
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried without labelling

9

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
R717 mixes very well with the oil, which easily returns to the compressor
An oil return line cannot be used in R717 systems because the oil is too hot

10

Nehéz

Which refrigerant can be detected with phenolphthalein paper?


R717
R744
R1234ze(E)
R1270

11

Nehéz

Which system may require manual oil recovery?


Secondary system using R744
Supercritical ‘booster’ system using R744
An R717 system
R744 cascade system

12

Nehéz

Which refrigerant is lighter than air?


R1234ze(E)
R744
R1270
R717

13

Nehéz

R717 is highly corrosive to:


aluminium
stainless steel
titanium
copper (and its alloys)

14

Nehéz

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500,000 ppm
5,000 ppm
500 ppm
50,000 ppm

15

Nehéz

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To lower the condensing pressure
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
Because they are cheaper
To increase the refrigerant charge

16

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


Diaphragm compressor
Rotary vane compressor
A reciprocating or screw compressor
Hermetic scroll

17

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


By increasing the condensing pressure
Solely by adjusting the oil volume
By unloading the cylinders or changing the rotational speed
By reducing the refrigerant charge

18

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By adjusting the oil level
By changing the type of oil
By closing the suction valve
By using a slide valve

19

Nehéz

When is two-stage compression used in NH₃ systems?


Only with water-cooled condensers
At small temperature differences
Only in small systems
At low evaporating temperatures (pressures) and high pressure ratios

20

Nehéz

What is the advantage of two-stage compression over single-stage compression?


Lower efficiency
Higher efficiency and lower discharge temperature
No need for a separator
Higher energy consumption

21

Nehéz

How does an evaporative condenser used in NH₃ systems work?


Operates without a fan
It transfers heat only to the air
It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency

22

Nehéz

What is the function of the liquid separator in an NH₃ system?


Increases the discharge temperature
Regulates the condensing pressure
It prevents liquid from entering the compressor
It separates oil from the refrigerant

23

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To maintain the correct refrigerant level and prevent the compressor from flooding
To control the condenser fan
To increase the oil volume
To reduce the condensing temperature

24

Nehéz

What is the role of the float switch in NH₃ systems?


It monitors the liquid level in the tank or separator
It regulates the condensation temperature
It controls the fan’s operation
It is used to detect leaks

25

Nehéz

What is a thermosyphon in NH₃ systems?


A type of safety valve
A defrosting device
An oil circulation pump
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling

26

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To increase the amount of refrigerant
Because the oil mixes only with water
Because NH₃ does not mix with most compressor oils
To reduce the pressure

27

Nehéz

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
To separate the oil from the refrigerant and return the oil to the compressor
Removing moisture from the system
To increase fan efficiency

28

Nehéz

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A pumped liquid-recirculation system
A glycol system
A direct-expansion (DX) system
An indirect system

29

Nehéz

What is the characteristic feature of a flooded evaporator system?


The evaporator contains a large amount of liquid, which improves heat transfer
No separator is used
The evaporator is filled exclusively with vapour
No level control is required

30

Nehéz

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In a direct system, there is no evaporator