F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Ťažká

What additional protective equipment will you use when brazing systems containing HC refrigerants?


Latex gloves
A flammable gas detector
A high-visibility vest
Ear defenders

2

Ťažká

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


It is a potential source of ignition
There is a risk of refrigerant leakage
The pressure switch setting will not be correct
Dust and moisture may enter

3

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


1 m
2 m
3 m
0.5 m

4

Ťažká

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


20 kg
9 kg
18 kg
33 kg

5

Ťažká

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


2.5 kg
0,494 kg
1.0 kg
10 kg

6

Ťažká

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Ignition-source-free pump, good ventilation, exhaust to a safe place
Place the pump directly on the floor, as low as possible
Such systems need not be evacuated before charging
Position the pump at least 3 m above floor level

7

Ťažká

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire extinguisher
Tinted safety goggles
Thick gloves
A fire blanket

8

Ťažká

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Recover the R32 to a vacuum and start desoldering immediately
Vent the R32 outdoors and purge the system
Vent the R32 outdoors, then fill and vent the system with nitrogen three times

9

Ťažká

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Electronic HFC leak detector
Soapy water solution
Leak detection foam
Electronic leak detector for flammable refrigerants

10

Ťažká

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


Different low-pressure switch setting
Different connection sizes
A flammable refrigerant recovery unit has no ignition sources
A different colour for the station

11

Ťažká

Which of the following is a source of ignition?


An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)
A sealed NTC temperature sensor
An Ex-certified fan motor

12

Ťažká

What particularly hazardous substance is formed when R32 burns?


Phosgene
Sulphur dioxide (SO₂)
Hydrogen chloride (HCl)
Hydrogen fluoride (HF)

13

Ťažká

What type of refrigerant is R1234ze(E)?


HCFC (hydrochlorofluorocarbon)
HC (hydrocarbon)
HFO (hydrofluoroolefin)
CFC (chlorofluorocarbon)

14

Ťažká

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, higher flammability
Higher toxicity, moderate flammability
Higher toxicity, higher flammability
Lower toxicity, moderate flammability

15

Ťažká

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.0 kg
4.93 kg
1.5 kg
0.285 kg

16

Ťažká

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 1.3
approx. 1.05–1.1
approx. 0.75
approx. 0.6

17

Ťažká

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they are more reliable
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they must be kept running continuously to disperse the leaking refrigerant
Because they are more energy-efficient

18

Ťažká

Why is the density difference between HC and HFC refrigerants important?


Because HCs must be charged much more slowly than HFCs
Because it determines the system's energy efficiency
An HC charge in kg is roughly half that of an HFC
Because HCs operate at much higher pressures

19

Ťažká

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


7
150
0.02
675

20

Ťažká

Which of the following is NOT a source of ignition?


A light switch
An Ex-certified fan motor
An unsealed mechanical pressure switch
An electrical switch

21

Ťažká

What is R290?


Propene (Propylene)
Butane
Isobutane
Propane

22

Ťažká

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


2.5 kg
1.2 kg
1.5 kg
150 g

23

Ťažká

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


The method of starting the compressor motor differs from that used with HFCs
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
A relay is never required for compressors using flammable refrigerants
It could be a source of ignition

24

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


3 m
10 m
5 m
1 m

25

Ťažká

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


approx. 17 kg
approx. 8 kg
20 kg
approx. 5.2 kg

26

Ťažká

How can a vacuum pump be used safely to evacuate a system containing R290?


Ignition-source-free pump, good ventilation, exhaust to a safe place
Place the pump directly on the floor, as low as possible
Position the pump at least 3 m above floor level
R290 systems need not be evacuated before charging

27

Ťažká

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
Tinted safety goggles
A fire blanket
Thick gloves

28

Ťažká

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Working outdoors is sufficient
Purge the system with compressed air
Such joints must never be desoldered; they must be cut with a pipe cutter
Ensure good ventilation and check the work area with a flammable gas detector

29

Ťažká

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 into the room and open a window
Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Vent the R1270 outdoors and start brazing immediately
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge

30

Ťažká

Which method should NOT be used to locate an R290 leak?


Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic leak detector designed for HFCs
Leak detection foam
An electronic detector for flammable refrigerants

31

Ťažká

Why can’t recovery stations designed for HFCs be used with R600a?


The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
They contain ignition sources
The recovery unit cannot withstand the working pressure of R600a
The oil in the recovery unit is not soluble in R600a

32

Ťažká

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


6.18 kg
618 kg
227 kg
2.27 kg

33

Ťažká

What type of refrigerant is R32?


Carbon dioxide
Hydrocarbon
Hydrofluoroolefin
Hydrofluorocarbon

34

Ťažká

What hazards do A2L refrigerants pose?


Higher toxicity, lower flammability
Higher toxicity, higher flammability
Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Lower toxicity, higher flammability

35

Ťažká

What hazard is associated with the combustion of HFO or HFC refrigerants?


Hydrogen fluoride (HF) is formed
Ozone is formed
Phosgene is formed
Nitrous oxide is formed

36

Ťažká

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About twice as large
About seven times as large
The same
About half

37

Ťažká

What is the GWP value for R32 according to Regulation (EU) 2024/573?


3
675
0
7

38

Ťažká

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because R290 is only used in systems below 150 g
Because of lower operating pressures
Because such systems never have liquid receivers

39

Ťažká

Why does the condenser fan run continuously in some systems using R1270?


To dilute the refrigerant in the event of a leak
To reduce energy consumption
To ensure that the discharge pressure never becomes excessive
To prevent the build-up of contaminants in the condenser

40

Ťažká

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It prevents liquid refrigerant from entering the compressor
It heats the refrigerant before the evaporator
It separates liquid from oil
It is used only to measure moisture

41

Ťažká

What is the function of an oil separator in systems using flammable or toxic refrigerants?


They are used solely to measure the moisture content of the refrigerant
It prevents liquid from entering the compressor
Heats the refrigerant before it enters the evaporator
Separates oil from the refrigerant and facilitates the return of oil to the compressor

42

Ťažká

Why do liquid and oil separators in CO₂ systems require particular attention?


Because CO₂ needs no lubrication, so oil separators are unnecessary
Because CO₂ is flammable and separators must not be used
Because of very high pressures – adequate PS and protection devices are required
Because sight glasses and level indicators must not be used in CO₂ systems

43

Ťažká

What is the critical pressure of CO₂ (R744)?


Approx. 31 bar
Approx. 74 bar (abs)
Approx. 10 bar
Approx. 120 bar

44

Ťažká

What characterises the transcritical process in CO₂ systems?


Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
It is irrelevant to system operation
It occurs only at low temperatures
Conventional condensation occurs

45

Ťažká

What characterises the subcritical CO₂ process?


The absence of condensation
Operation above the critical point
The conventional condensation process below the critical point
The absence of evaporation

46

Ťažká

When can dry ice (solid CO₂) form?


During normal operation of the system
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system
At high temperature
At high pressure

47

Ťažká

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
No risk
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
Pressure reduction

48

Ťažká

How does CO₂ saturation pressure change as temperature increases?


It remains the same
It first decreases, then increases
It increases rapidly
It decreases

49

Ťažká

What happens to CO₂ above the critical point?


It turns into a solid
It ceases to conduct heat
It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a liquid

50

Ťažká

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator needs no expansion valve, a flooded one does
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
A dry-expansion evaporator always has a lower pressure than a flooded one

51

Ťažká

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Below atmospheric (approx. 0.7 bar abs at −40 °C)
Atmospheric pressure, approx. 1 bar abs
Positive pressure of 5–10 bar
Positive pressure of 10–20 bar

52

Ťažká

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They are climate- and environment-neutral
They are readily biodegradable
They cause rapid cooling of the atmosphere

53

Ťažká

How is oil managed in R717 systems?


Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil requires no monitoring
Oil can be mixed with any refrigerant
Oil has no effect on system operation

54

Ťažká

What should be done with contaminated R717?


Purify it or send it for disposal in accordance with regulations
Continue to use it without restriction
Release it into the atmosphere
Dilute it with water and reuse it

55

Ťažká

What should be done if an NH₃ leak is detected?


Increase the pressure in the system
Carry on working with the room door open
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Carry on working wearing a dust mask

56

Ťažká

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They store the refrigerant
They increase the pressure in the system
Neutralise ammonia through absorption in a liquid (e.g. water)

57

Ťažká

How should the system be prepared before filling with R717?


Simply start it up
There is no need to check it
Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level

58

Ťažká

What are the transport requirements for R717?


It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried without labelling
Transport is not regulated
It can be carried in open containers

59

Ťažká

What is the main characteristic of R744 (CO₂) refrigeration systems?


Low energy efficiency under all conditions
Very high operating pressures
No need for control
Low operating pressures

60

Ťažká

What are the requirements for piping materials in CO₂ systems?


They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)
It doesn't matter
Only plastics
Any material may be used

61

Ťažká

How does a booster system work in CO₂ installations?


It reduces evaporator pressure
It reduces the refrigerant quantity
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It is used to store refrigerant

62

Ťažká

Why is pressure optimisation in CO₂ systems crucial?


It reduces the ambient temperature
It doesn’t matter
It reduces the amount of refrigerant
It enables the system to achieve maximum energy efficiency in transcritical mode

63

Ťažká

What role does parallel compression play in CO₂ systems?


It lowers the ambient temperature
It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It has no significance
It increases energy consumption

64

Ťažká

How does an ejector work in a CO₂ system?


It increases the amount of refrigerant
Stores the refrigerant
It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It lowers the evaporator temperature

65

Ťažká

What is the function of liquid ejectors in CO₂ systems?


They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They reduce atmospheric pressure
They increase the amount of oil
They raise the refrigerant temperature

66

Ťažká

What are the characteristics of partially flooded systems in CO₂ systems?


The presence of liquid in the evaporator, which improves heat transfer and efficiency
Lack of regulation
Low operating pressure
The absence of liquid in the evaporator

67

Ťažká

What is the main risk associated with standstill pressure in CO₂ systems?


A drop in temperature
Increased efficiency
A decrease in refrigerant quantity
A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)

68

Ťažká

How is standstill pressure limited in CO₂ systems?


By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By completely shutting down the system and power supply
By raising the plant-room temperature
By increasing the refrigerant charge

69

Ťažká

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


A drop in system temperature
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Normal system operation
Improved efficiency

70

Ťažká

What must the label of a flammable refrigerant cylinder include?


Information about the cylinder owner
Only the net weight
The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Only the refrigerant name

71

Ťažká

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It reduces system efficiency
It has no significant effect on safety
It may lead to the wrong oil being selected
It may lead to the use of tools that are ignition sources

72

Ťažká

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Gross weight and batch number
Manufacturer’s name and country of origin
Cylinder colour and date of manufacture
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number

73

Ťažká

What is the purpose of gas detectors in a room with a refrigeration system?


Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Controlling compressor capacity
Monitoring pipe pressure
Measuring refrigerant temperature

74

Ťažká

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Only after a leak has occurred
Once every 5 years
Before every start-up of the unit

75

Ťažká

Where should a gas detector be located according to EN 378?


Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Near the control panel
Anywhere in the room
Only at the room entrance

76

Ťažká

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


The colour of pipes and hoses
Only the compressor power
Only that the air filter is new
The presence of health and safety signage, adequate ventilation and gas detectors

77

Ťažká

What are the requirements for emergency exits from a refrigeration machinery room?


One exit with a sign stating the refrigerant type is sufficient
Outward-opening doors and signed escape routes (number of exits per the standard)
At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed

78

Ťažká

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


Restricting room ventilation
Charging above the nameplate quantity
Omitting the filter-drier
A thorough tightness test and evacuation (dehydration) of the system

79

Ťažká

Why is it important to limit the refrigerant charge in HC systems?


It lowers the temperature
It doesn't matter
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It increases capacity

80

Ťažká

Which safety class applies to R744?


A1
A3
B2L
A2.

81

Ťažká

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…saturated vapour at intermediate pressure
…a supercritical fluid
…a subcooled liquid
…a two-phase mixture at intermediate pressure

82

Ťažká

In R744 transcritical systems, the gas cooler outlet valve controls:


The inlet temperature to the gas cooler
The gas cooler fans
The pressure in the gas cooler
The outlet temperature of the gas cooler

83

Ťažká

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot
R717 mixes very well with the oil, which easily returns to the compressor
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717

84

Ťažká

What is the main reason for using K65 copper tubing in some R744 systems?


They bend easily
They can withstand higher pressures
They come in a wider range of diameters
They have good low-temperature performance

85

Ťažká

Which statement about installing Schrader valves is correct?


Schrader valves must not be used in R744 systems
All Schrader cores are suitable for all refrigerants
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Hydrocarbons leak through Schrader valves

86

Ťažká

Which refrigerant can be detected with phenolphthalein paper?


R1234ze(E)
R744
R1270
R717

87

Ťažká

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure higher, subcooling higher
Discharge pressure higher, subcooling lower
Discharge pressure lower, subcooling higher

88

Ťažká

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It has a distinctive odour that helps locate the leak
It reacts with refrigerant residues, producing a visible colour change
Its small atoms pass easily through leaks and are detected
It has a higher pressure than pure nitrogen in the same cylinder

89

Ťažká

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To prevent the drain valve on the receiver from opening
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To charge R744 more slowly and measure it more accurately
To avoid damaging the compressor with liquid CO₂

90

Ťažká

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Formation of hydrogen fluoride and hydrofluoric acid
Formation of carbonic acid, which damages the system
Reduced cooling capacity
Excessive discharge pressure

91

Ťažká

Which system may require manual oil recovery?


An R717 system
R744 cascade system
Supercritical ‘booster’ system using R744
Secondary system using R744

92

Ťažká

The pressure of R744 at a saturation temperature of 20 °C is approx.


25 bar g
56 bar g
90 bar g
14 bar g

93

Ťažká

Which refrigerant is lighter than air?


R717
R1234ze(E)
R1270
R744

94

Ťažká

What hazards are associated with a safety group A3 refrigerant?


Higher toxicity, no flame propagation
Higher flammability, lower toxicity
Lower flammability, lower toxicity
Lower toxicity, no flame propagation

95

Ťažká

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


3922
0
6
675

96

Ťažká

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, room volume
Practical limit, height of the indoor unit, floor area
Lower flammability limit, room volume
Lower flammability limit, height of the indoor unit, floor area

97

Ťažká

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


Similar
About half
About 1.5 times larger
About 6 times larger

98

Ťažká

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…approx. 27.5 bar g
…the same as the high-pressure switch setting
…the same as the relief valve set pressure
…higher than the maximum allowable pressure (PS) of the low-pressure stage

99

Ťažká

What is the correct definition of critical temperature?


The temperature at which a substance changes from a gaseous to a solid state
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature above which there are no distinct liquid and gaseous phases
The temperature at which, for certain substances, electrical resistance is zero

100

Ťažká

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat at constant temperature and pressure
…rejects heat during a phase change
…rejects heat as its temperature falls
…rejects heat as its pressure falls

101

Ťažká

R717 is highly corrosive to:


aluminium
titanium
copper (and its alloys)
stainless steel

102

Ťažká

What can be the effect of a relief valve lifting repeatedly?


The valve stays fully open permanently
The valve no longer opens
The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease

103

Ťažká

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = T₁/(p₁ × T₂)
p₂ = T₂/(p₁ × T₁)
p₂ = (p₁ × T₂)/T₁
p₂ = (p₁ × T₁)/T₂

104

Ťažká

What is the recommended pre-alarm level for fixed leak detection systems for R717?


5,000 ppm
500,000 ppm
500 ppm
50,000 ppm

105

Ťažká

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To lower the condensing pressure
Because they are cheaper
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To increase the refrigerant charge

106

Ťažká

Which type of compressor is most commonly used in large ammonia systems?


Hermetic scroll
A reciprocating or screw compressor
Rotary vane compressor
Diaphragm compressor

107

Ťažká

How is the capacity of a piston compressor regulated in NH₃ systems?


By unloading the cylinders or changing the rotational speed
By reducing the refrigerant charge
Solely by adjusting the oil volume
By increasing the condensing pressure

108

Ťažká

How is the capacity of a screw compressor most commonly controlled?


By changing the type of oil
By closing the suction valve
By adjusting the oil level
By using a slide valve

109

Ťažká

When is two-stage compression used in NH₃ systems?


Only in small systems
Only with water-cooled condensers
At small temperature differences
At low evaporating temperatures (pressures) and high pressure ratios

110

Ťažká

What is the advantage of two-stage compression over single-stage compression?


Higher energy consumption
No need for a separator
Higher efficiency and lower discharge temperature
Lower efficiency

111

Ťažká

How does an evaporative condenser used in NH₃ systems work?


Operates without a fan
It transfers heat only to the air
It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency

112

Ťažká

What is the function of the liquid separator in an NH₃ system?


Regulates the condensing pressure
It prevents liquid from entering the compressor
It separates oil from the refrigerant
Increases the discharge temperature

113

Ťažká

What is the purpose of monitoring the liquid level in the separator?


To increase the oil volume
To reduce the condensing temperature
To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding

114

Ťažká

What is the role of the float switch in NH₃ systems?


It monitors the liquid level in the tank or separator
It regulates the condensation temperature
It controls the fan’s operation
It is used to detect leaks

115

Ťažká

What is a thermosyphon in NH₃ systems?


A defrosting device
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
A type of safety valve
An oil circulation pump

116

Ťažká

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


Because NH₃ does not mix with most compressor oils
To increase the amount of refrigerant
Because the oil mixes only with water
To reduce the pressure

117

Ťažká

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
Removing moisture from the system
To increase fan efficiency
To separate the oil from the refrigerant and return the oil to the compressor

118

Ťažká

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A pumped liquid-recirculation system
A glycol system
A direct-expansion (DX) system
An indirect system

119

Ťažká

What is the characteristic feature of a flooded evaporator system?


No level control is required
The evaporator is filled exclusively with vapour
No separator is used
The evaporator contains a large amount of liquid, which improves heat transfer

120

Ťažká

What is the main difference between a direct and an indirect system?


In a direct system, there is no evaporator
In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In an indirect system, NH₃ flows directly into the space being cooled

121

Ťažká

Which parts of a refrigeration system should be given particular attention during a leak check?


Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Compressor and receiver connections, because the pressure is highest there
Only compressor connections, because they are the only parts subject to vibration
Only condenser connections, because the refrigerant is liquid there

122

Ťažká

Leak checks can be carried out using various methods. Which pair is correct?


Material quality control methods and electronic methods
Methods with and without quality control of supplies
Physical and chemical methods
Direct and indirect methods

123

Ťažká

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


Any leak-testing specialist
An employee appointed by the owner of the installation
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
A person who has carried out such checks before

124

Ťažká

What conditions must be met to use UV dye for leak checking?


A UDT authorisation for pressure testing is required
It is sufficient to have a UV lamp, dye and safety goggles
Manufacturer approval of the method and a certificate covering breaking into the circuit
It is sufficient that introducing dye into the circuit is technically feasible

125

Ťažká

Which leak-checking methods are considered direct methods?


Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution
Pressure-change measurement and immersion in water
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions

126

Ťažká

What do indirect leak-checking methods involve?


Ultrasonic measurement
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Leak detection with UV dye
Leak detection with an electronic detector

127

Ťažká

What does a vacuum (decay) test involve?


The pump runs continuously to hold the required vacuum for the test
With the pump running, you watch the vacuum gauge reading
After isolating the pump, you check whether the system pressure rises
The pump is restarted every time the system pressure rises

128

Ťažká

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


On initial commissioning.
At least once every 12 months.
Only when servicing the unit.
Once every six months.

129

Ťažká

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Once every six months.
Only when servicing the unit.
On initial commissioning.
At least once every 12 months.

130

Ťažká

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the charge is 100 kg or more of ozone-depleting substances
the equipment contains a flammable refrigerant in any quantity
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the equipment operates in an enclosed space

131

Ťažká

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Leak checking with a fluorescent dye introduced into the circuit
Measurement with a handheld electronic detector
Visual inspection
Checking with a foaming solution

132

Ťažká

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At any time.
Between 24 hours and 1 month after the repair.
At the next periodic inspection.
Immediately after the repair.

133

Ťažká

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every 12 months
Every month
Every 6 months

134

Ťažká

What is the basis of the GWP values in Regulation (EU) 2024/573?


For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR6 for all substances
AR4 for all substances
Each Member State sets its own GWP values

135

Ťažká

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


At least every 12 months (5.22 t CO₂ eq)
No checks required (below 3 kg)
Every 3 months
Every 6 months

136

Ťažká

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


When it contains less than 5 t CO₂ eq
Always, regardless of charge
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases
Never – hermetically sealed equipment is always checked

137

Ťažká

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


No – HFOs are not subject to leak checks
Yes – every 12 months, because its GWP is low
Yes – at least every 6 months (every 12 months with a leakage detection system)
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq

138

Ťažká

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes, if the equipment has a leakage detection system
Yes – the ban applies only to equipment ≥40 t CO₂ eq
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes – bans apply only to new equipment

139

Ťažká

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
No – the ban covers all HFCs
No – the ban covers all refrigerants with GWP ≥ 750
Only with reclaimed refrigerant

140

Ťažká

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes – the ban applies from 2029
Yes, if the unit is hermetically sealed
Yes – the ban applies only to units >12 kW
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned

141

Ťažká

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2035
From 1 January 2027
From 1 January 2029
From 1 January 2025

142

Ťažká

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Ozone
Trifluoroacetic acid (TFA)
Carbon dioxide
Carbonic acid

143

Ťažká

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


1.5 kg
1.2 kg
13 × LFL ≈ 494 g
150 g

144

Ťažká

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 1.5 kg
approx. 13.8 kg
approx. 0.46 kg
approx. 4.6 kg

145

Ťažká

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


1000 kg
20 kg
Unlimited
333 kg

146

Ťažká

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 0.15 kg
approx. 13 kg
approx. 4.94 kg
approx. 0.99 kg

147

Ťažká

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
Gas cooler pressure drops – extra charge is added
CO₂ freezes in the gas cooler – heaters are used
Efficiency does not depend on climate