F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Difficult

What additional protective equipment will you use when soldering systems containing HC refrigerants?


Fire blanket
Tinted safety goggles
Flammable gas detector
High-visibility jacket

2

Difficult

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


There is a risk of refrigerant leakage
Dust and moisture may enter
It is a potential source of ignition
The pressure switch setting will not be correct

3

Difficult

What is the minimum distance from the work area where HC refrigerants are used at which there must be no sources of ignition?


3 m
0.5 m
2 m
1 m

4

Difficult

What is the maximum safe charge for a recovery cylinder with R32 refrigerant, if it can be charged with 20 kg of R410A?


9 kg
33 kg
18 kg
20 kg

5

Difficult

According to EN 378, what is the maximum charge of an A3 refrigerant for a display unit (hermetic, with an internal condenser) located in the ground-floor retail area of a supermarket?


2.5 kg
10 kg
1.0 kg
1.5 kg

6

Difficult

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Use an ATEX-certified vacuum pump in a well-ventilated area
Position the vacuum pump 3 metres above floor level
Fit a long hose to the pump outlet to remove HC away from the system
There is no need to evacuate such systems

7

Difficult

What protective equipment must you have in your car when transporting flammable substances?


Tinted safety goggles
Thick gloves
A fire extinguisher
Fire blanket

8

Difficult

How would you remove the refrigerant from a 10kg R32 water chiller, located outdoors, before unsoldering the connections?


Recover the R32 until a vacuum is achieved
Vent the R32 to the outside and drain the system
Vent the R32 to the outside; charge the system with nitrogen until an overpressure is achieved, vent and drain the system twice, charge the system with nitrogen a third time and vent
Recover the R32 until a vacuum is achieved, then charge the system with nitrogen to a relative pressure of 0.1 bar g

9

Difficult

Which of the following leak detection methods cannot be used to locate an HC refrigerant leak?


Electronic HFC leak detector
Electronic leak detector for flammable refrigerants
Leak detection foam
Soapy water solution

10

Difficult

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


A flammable refrigerant recovery unit has no ignition sources
A different colour for the station
Different connection sizes
Different low-pressure switch setting

11

Difficult

Which of the following is a source of ignition?


‘n’ type thermostat
Defrost heating element
Contactor
Ex-certified evaporator fan motor

12

Difficult

What substance is produced when R32 is burnt?


Hydrogen fluoride
Carbon monoxide
Phosgene
Hydrochloric acid

13

Difficult

What type of refrigerant is R1234ze?


Hydrochlorofluoro-hydrocarbon
Chloro-fluoro-hydrocarbon
Hydrofluoroolefin
Hydrocarbon

14

Difficult

What hazards does a Group A3 refrigerant pose?


Low toxicity, moderate flammability
High toxicity, moderate flammability
Low toxicity, highly flammable
High toxicity, high flammability

15

Difficult

According to EN 378, what is the maximum charge of R290 in a cold store measuring 5 m x 3 m x 2.5 m in height (the LFL for R290 is 0.038 kg/m³)?


4.93 kg
0.285 kg
1.0 kg
1.5 kg

16

Difficult

What is the cooling capacity of R32 compared to R410A?


130%
75%
60%
105%

17

Difficult

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they must be kept running continuously to disperse the leaking refrigerant
Because they are more energy-efficient
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they are more reliable

18

Difficult

Why is the difference in density between HC and HFC refrigerants important?


Because it affects the charge weight
Because it affects energy efficiency
Because it affects the charging rate
Because it increases operating pressures

19

Difficult

What is the GWP value for R290?


675
A. 0.02
7
3

20

Difficult

Which of the following is not a source of ignition?


Electrical switch
Light switch
Open mechanical pressure switch
An Ex-certified fan motor

21

Difficult

What is R290?


Ethane
Butane
Propylene
Propene

22

Difficult

According to EN 378, what is the maximum HC refrigerant charge for a display unit (hermetic system with an internal condenser) located in the ground-floor shopping area of a supermarket?


2.5 kg
1.0 kg
1.5 kg
150 g

23

Difficult

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


The method of starting the compressor motor differs from that used with HFCs
A relay is never required for compressors using flammable refrigerants
It could be a source of ignition
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs

24

Difficult

What is the minimum distance from the work area where HC refrigerants are used at which there must be no sources of ignition?


1 m
10 m
3 m
5 m

25

Difficult

What is the safe charge for a recovery cylinder with R290 refrigerant, if it can be charged with 10 kg of R404A?


3.6 kg
20 kg
17 kg
8 kg

26

Difficult

How can a vacuum pump be used safely to evacuate a system containing R290?


There is no need to evacuate systems containing R290
Fit a long hose to the pump outlet to remove HC away from the system
Position the vacuum pump 3 metres above floor level
Use an ATEX-certified vacuum pump in a well-ventilated area

27

Difficult

In accordance with ADR regulations, what protective equipment must you have in your vehicle when transporting flammable refrigerants?


Tinted safety goggles
A fire extinguisher
Thick gloves
Fire blanket

28

Difficult

How do you ensure it is safe to light the torch needed to desolder joints in a system that has been evacuated of flammable refrigerant?


Ensure the area is well ventilated and use a flammable gas detector to check the area
Work outdoors
You must not desolder joints on a system containing a flammable refrigerant; they must be cut using a pipe cutter
Purge the system with oxygen-free nitrogen

29

Difficult

How would you remove the refrigerant from a system containing 100 g of R1270 so that it is ready for the joints to be desoldered?


Vent the R1270 to the outside; charge the system with nitrogen until an overpressure is reached, vent and evacuate the system twice, charge the system with nitrogen a third time and vent
Recover the R1270 until a vacuum is achieved
Vent the R1270 to the outside and drain the system
Recover the R1270 until a vacuum is achieved, then charge the system with nitrogen to a relative pressure of 0.1 bar g

30

Difficult

Which of the following leak detection methods cannot be used to locate a leak of R290 refrigerant?


Leak detection foam
Electronic leak detector for flammable refrigerants
Fluorescent dye and a UV lamp
Electronic HFC leak detector

31

Difficult

Why can’t recovery stations designed for HFCs be used with R600a?


The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
It contains ignition sources
The oil in the recovery unit is not soluble in R600a
The recovery unit cannot withstand the working pressure of R600a

32

Difficult

According to EN 378, what is the maximum charge of R1234ze in a cold store measuring 5 m x 3 m x 2.5 m in height (the LFL for R1234ze is 0.303 kg/m³)?


2.27 kg
618 kg
6.18 kg
227 kg

33

Difficult

What type of refrigerant is R32?


Hydrocarbon
Carbon dioxide
Hydrofluorocarbon
Hydrofluoroolefin

34

Difficult

What hazards do A2L refrigerants pose?


Low toxicity, high flammability
High toxicity, moderate flammability
Low toxicity, moderate flammability
High toxicity, high flammability

35

Difficult

What danger is associated with the combustion of HFO or HFC refrigerants?


Hydrogen fluoride is produced
Nitrous oxide is produced
Phosgene is produced
Citric acid is produced

36

Difficult

What is the approximate displacement volume required for a compressor running on R600a compared to one running on R134a to achieve the same cooling capacity?


Twice
Half
The same
Seven times

37

Difficult

What is the GWP value for R32?


675
0
7
3

38

Difficult

Why is the accuracy of the charge weight more important for systems critically charged with R290 compared to those using HFCs


Due to lower operating pressures
Because R290 is only used in systems with a charge of less than 150g
Because these systems never have liquid receivers
The charge mass is significantly lower than in an HFC system, as the density is much lower

39

Difficult

Why does the condenser fan run continuously in some systems using R1270?


To prevent the build-up of contaminants in the condenser
To dilute the refrigerant in the event of a leak
To reduce energy consumption
To ensure that the discharge pressure never becomes excessive

40

Difficult

What is the role of the liquid separator in systems using flammable or toxic refrigerants?


Heats the refrigerant before it enters the evaporator
They are used solely to measure the moisture content of the refrigerant
It prevents liquid from entering the compressor
It separates the liquid from the oil

41

Difficult

What is the function of an oil separator in systems using flammable or toxic refrigerants?


Separates oil from the refrigerant and facilitates the return of oil to the compressor
They are used solely to measure the moisture content of the refrigerant
It prevents liquid from entering the compressor
Heats the refrigerant before it enters the evaporator

42

Difficult

Why do CO₂ refrigeration systems require special attention when separating liquid and oil?


CO₂ operates at high pressure, which increases the risk of compressor failure and leaks
CO₂ does not require lubrication, so separators are unnecessary
CO₂ is flammable, so separators cannot be used
CO₂ cannot be used in systems with sight glasses

43

Difficult

What is the critical pressure of CO₂ (R744)?


Approximately 120 bar
Approximately 31 bar
Approximately 10 bar
Approximately 74 bar

44

Difficult

What characterises the transcritical process in CO₂ systems?


The system operates above the critical point and the refrigerant does not condense in the conventional manner
It occurs only at low temperatures
It is irrelevant to the operation of the system
Conventional condensation occurs

45

Difficult

What characterises the subcritical CO₂ process?


The conventional condensation process below the critical point
The absence of condensation
The absence of evaporation
Operation above the critical point

46

Difficult

What is the log(p)-h diagram for CO₂ used for?


To regulate pressure
To detect leaks
To measure temperature
For analysing thermodynamic processes in a refrigeration system

47

Difficult

What can be read from the log(p)-h graph?


Only the temperature
Pressure, enthalpy, temperature and state of the refrigerant
Only the humidity
Only the amount of refrigerant

48

Difficult

What are CO₂ saturation tables used for?


To regulate the compressor
To measure humidity
To determine the relationship between temperature and pressure at saturation
To determine the oil quantity

49

Difficult

What does the CO₂ saturation state mean?


Dry ice state
A state in which the refrigerant is only a gas
A state of high pressure
Equilibrium between the liquid and vapour phases

50

Difficult

When can dry ice (solid CO₂) form?


At high pressure
At high temperature
In the event of a sudden drop in pressure and temperature below the triple point
During normal operation of the system

51

Difficult

What risks are associated with the formation of dry ice in a CO₂ system?


Pressure reduction
No risk
Improved efficiency
Blocked pipes and system damage

52

Difficult

How does the CO₂ pressure change as the temperature rises?


It decreases
It remains the same
Rises sharply
It first decreases, then increases

53

Difficult

Why is understanding the log(p)-h graph particularly important for CO₂?


It doesn’t matter
It only applies to NH₃
It is only used for design purposes
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis

54

Difficult

What happens to CO₂ above the critical point?


It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a solid
It ceases to conduct heat
It turns into a liquid

55

Difficult

Why do CO₂ systems require precise pressure control?


Due to significant pressure changes with temperature fluctuations
Because there are no valves
Due to low pressures
They do not require control

56

Difficult

What is the main difference between a dry evaporator and a flooded evaporator?


A dry evaporator allows the entire refrigerant to evaporate in the pipe upstream of the compressor; in a flooded evaporator, part of the refrigerant remains in a liquid state within the evaporator
A dry evaporator is filled with refrigerant liquid, whilst a flooded evaporator is filled with gas
A dry evaporator has a lower operating pressure than a flooded one
A dry evaporator does not require an expansion valve, whereas a flooded one does

57

Difficult

What is the typical pressure in deep-freezing systems (below −40 °C) for an evaporator in a system using R717?


Atmospheric pressure, approximately 1 bar
Positive pressure, in the range of 5–10 bar
A pressure varying between 10 and 20 bar
Negative pressure (vacuum), below 0 bar

58

Difficult

Why are PFAS substances formed as a result of the decomposition of certain F-gases problematic?


They cause rapid cooling of the atmosphere
They are persistent, accumulate in the environment and may be toxic
They are readily biodegradable, so they only pollute the environment for a short time
They are climate-neutral

59

Difficult

What is the basic requirement when charging a system with R717 (NH₃)?


Charging can be carried out without personal protective equipment
Charging should take place in a well-ventilated area using appropriate personal protective equipment
NH₃ can be charged together with air
Charging must only take place at temperatures below 0°C

60

Difficult

How should oil be handled in systems using R717?


Oil can be mixed with any refrigerant
Oil has no effect on the system’s operation
The oil should be checked regularly and any excess removed from the lower parts of the units to prevent reduced heat transfer and leaks
The oil does not require any monitoring

61

Difficult

What is the correct procedure for recovering R717 from a system?


Recovery is not required
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The refrigerant can be drained into the sewer system
The gas can be released into the atmosphere

62

Difficult

How should R717 (NH₃) be stored?


Near heat sources
In unmarked plastic containers
In sealed, labelled containers, in a cool and well-ventilated place
In any open containers

63

Difficult

What should be done in the event of R717 contamination?


Release into the atmosphere
Add water to dilute it
The refrigerant must be purified or sent for disposal in accordance with regulations
Continue to use without restriction

64

Difficult

What is the main hazard associated with an R717 leak during maintenance work?


Toxic to humans and may cause chemical burns
No risk whatsoever
Increased cooling efficiency
Damage to electrical equipment only

65

Difficult

What action should be taken if an NH₃ leak is detected?


Close your eyes and carry on working
Evacuate personnel immediately and remove the source of the leak, if it is safe to do so
Increase the pressure in the system
Ignore it and carry on working

66

Difficult

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They increase the pressure in the system
Neutralises ammonia through absorption in a liquid (e.g. water)
They store the refrigerant

67

Difficult

How should the system be prepared before filling with R717?


Simply start it up
The pressure must be increased above the standard level
Check for leaks, remove air and moisture, and create a vacuum
There is no need to check it

68

Difficult

What are the transport requirements for R717?


It can be transported in open containers
It can be transported without labelling
Transport is not subject to regulations
Must be transported in suitable, labelled containers in accordance with ADR regulations

69

Difficult

What personal protective equipment is required when working with NH₃?


Only a safety helmet
No requirements
Safety goggles, gloves and respiratory protective equipment
Workwear only

70

Difficult

What is the main characteristic of R744 (CO₂) refrigeration systems?


Low energy efficiency
Very high operating pressures
No need for regulation
Low operating pressures

71

Difficult

What are the requirements for piping materials in CO₂ systems?


They must be able to withstand high pressures (e.g. high-grade steel)
They may be made of any material
They must be made exclusively from plastics
It does not matter

72

Difficult

How does a booster system work in CO₂ installations?


It utilises two stages of compression (low and medium pressure) in a single system
It reduces the amount of refrigerant
It is used to store the refrigerant
It reduces the pressure in the evaporator

73

Difficult

What is the function of high-pressure control valves in CO₂ systems?


They are used to store the refrigerant
They control the pressure on the high-pressure side and optimise system operation
They regulate oil flow
They lower the evaporator temperature

74

Difficult

Why is pressure optimisation in CO₂ systems crucial?


It enables the system to achieve maximum energy efficiency
It reduces the amount of refrigerant
It reduces the ambient temperature
It doesn’t matter

75

Difficult

What role do parallel-operating compressors play in CO₂ systems?


It does not matter
They lower the ambient temperature
They enable gas recovery from the medium-pressure stage and improve efficiency
They increase energy consumption

76

Difficult

How does an ejector work in a CO₂ system?


Stores the refrigerant
It increases the amount of refrigerant
It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It lowers the evaporator temperature

77

Difficult

What is the function of liquid ejectors in CO₂ systems?


They increase the amount of oil
They raise the refrigerant temperature
They reduce atmospheric pressure
They assist with liquid recovery and improve evaporator feed

78

Difficult

What are the characteristics of partially flooded systems in CO₂ systems?


Lack of regulation
Low operating pressure
The presence of liquid in the evaporator, which improves heat transfer and efficiency
The absence of liquid in the evaporator

79

Difficult

What is the main risk associated with static pressure in CO₂ systems?


Increased efficiency
A rise in pressure resulting from the refrigerant heating up whilst at rest
A decrease in refrigerant quantity
A drop in temperature

80

Difficult

How can standstill pressure in CO₂ systems be reduced?


By using parallel compressors and external cooling systems
By shutting down the system completely
By increasing the refrigerant charge
By increasing the temperature

81

Difficult

What does ‘stagnation’ of a refrigeration system mean in the context of CO₂?


A lack of refrigerant flow, which can lead to increased pressure and safety risks
A drop in temperature
Improved efficiency
Normal system operation

82

Difficult

Why do CO₂ systems require more advanced automation than traditional systems?


Due to the need for precise control of pressure and temperature
They do not require automation
Due to low pressures
Because there are no valves

83

Difficult

What must be included on the label of a cylinder containing a flammable refrigerant?


Net weight only
Agent name only
The name of the refrigerant, the hazard symbol and basic safety information
Information about the cylinder owner

84

Difficult

Why does the absence of a ‘flammable agent’ label on the system pose a significant hazard?


It may lead to the incorrect selection of oil
It has no significant impact on safety
It reduces the system’s efficiency
It may lead to the use of tools that are a source of ignition

85

Difficult

Which set of information on the label of a flammable agent cylinder is crucial from a safety perspective?


Manufacturer’s name and country of origin
Cylinder colour and date of manufacture
Name of the substance, hazard pictogram, UN number
Gross weight and batch number

86

Difficult

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is required only in technical rooms
Colour-coding of pipes is sufficient
The labelling must indicate the type of substance and the flammability hazard
Labelling is not required for hermetically sealed systems

87

Difficult

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


No impact on safety
Merely a reduction in efficiency
Risk of leakage and the formation of an explosive mixture
Merely installation difficulties

88

Difficult

What is the purpose of installing gas detectors in a room with a refrigeration system?


Early detection of refrigerant leaks and prevention of health risks
Measuring the refrigerant temperature
Regulating compressor capacity
Monitoring pipe pressure

89

Difficult

How often should gas detection sensors in the service room be checked?


Before each start-up of the unit
In accordance with the manufacturer’s instructions and applicable health and safety regulations
Once every 5 years
Only after a leak has occurred

90

Difficult

Where should a gas detector be positioned in accordance with EN 378?


Near the control panel
On the ceiling if the gas is lighter or heavier than air; near the floor if it is lighter or heavier
Only at the entrance to the room
Anywhere in the room

91

Difficult

How should an employee respond when a gas alarm is triggered?


Switch off the system and wait for the alarm to stop
Leave the room immediately and notify their supervisor
Reduce the pressure in the system
Carry on working until they see a leak

92

Difficult

What safety checks should be carried out when installing a new refrigeration system?


Only the compressor power
The colour of pipes and hoses
Is the air filter new?
The presence of health and safety signage, adequate ventilation and gas detectors

93

Difficult

Gas detectors should be installed in rooms where:


The amount of refrigerant exceeds a specified permissible threshold
Any refrigerant is present, regardless of the quantity
The room is less than 5 m²
Ventilation is natural

94

Difficult

What is the minimum number of emergency exits in a plant room (refrigeration plant room) and how should they be signposted?


One exit, clearly marked in the direction of escape
One exit with an information sign about the refrigerant
At least two exits, but signage is optional
Exits do not need to be signposted if the room is small

95

Difficult

Which measure, when installing a system using a flammable refrigerant, improves its energy efficiency?


No leak test
Restriction of ventilation
Thorough leak testing and vacuuming
Increasing the refrigerant charge

96

Difficult

How do leaks affect systems using flammable refrigerants?


They improve efficiency
They lower the temperature
They cause refrigerant loss, reduced efficiency and a fire hazard
Have no effect

97

Difficult

Why is it important to limit the amount of refrigerant in HC systems?


It has no effect
It lowers the temperature
It reduces the risk of explosion and improves the system’s operational safety
It increases efficiency

98

Difficult

Why is the cleanliness of heat exchangers in HC systems important?


It improves heat transfer and reduces energy consumption
It doesn’t matter
It increases the pressure
Causes leaks

99

Difficult

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Lack of servicing
Regular checks for leaks and operating parameters
Increasing the refrigerant charge
Disabling safety devices

100

Difficult

How does the correct selection of components affect a system using a flammable refrigerant?


It lowers the temperature
It ensures safe and optimal operation and minimises energy losses
It doesn’t matter
It increases the amount of refrigerant

101

Difficult

Why is it important to use the correct service tools in HC systems?


It increases energy consumption
Causes leaks
It ensures operational safety and reduces refrigerant losses
It doesn’t matter

102

Difficult

How does pipe insulation affect the efficiency of systems containing HC?


It increases the pressure
It doesn’t matter
Causes leaks
It reduces energy losses and improves efficiency

103

Difficult

Which safety class applies to R744?


A1
A2
A3
B2L

104

Difficult

In an R744 system operating in supercritical mode, the refrigerant entering the evaporator expansion valve is...


A two-phase mixture at intermediate pressure
A supercritical fluid
Saturated vapour at intermediate pressure
A subcooled liquid

105

Difficult

In R744 supercritical systems, the gas cooler outlet valve controls:


The outlet temperature of the gas cooler
The inlet temperature to the gas cooler
The pressure in the gas cooler
The gas cooler fans

106

Difficult

Which statement best describes the behaviour of R717 and mineral compressor oil?


In an R717 system, a return oil line cannot be used because the oil is too hot
R717 does not mix with compressor oil, so the oil remains in the system on the low-pressure side as a layer beneath the R717
R717 mixes very well with compressor oil and easily returns to the compressor
R717 does not mix with compressor oil, so the oil remains in the system on the high-pressure side as a layer above the R717

107

Difficult

What is the main reason for using K65 copper tubing in some R744 systems?


They come in a wider range of diameters
They bend easily
They can withstand higher pressures
They have good low-temperature performance

108

Difficult

Which of the following statements is correct regarding the installation of Schrader valves?


Schrader valves must not be used in R744 systems
Hydrocarbons leak through Schrader valves
When brazing the valve body to the system, the core must be removed, then refitted and tightened to the correct torque
All Schrader valve cores are suitable for all refrigerants

109

Difficult

Which refrigerant can be detected using phenolphthalein paper?


R717
R1270
R1234ze
R744

110

Difficult

How does a refrigerant shortage affect the high-pressure side of the system (without discharge pressure regulation)?


Discharge pressure will be higher, and the degree of subcooling will be lower
Discharge pressure will be higher, and the degree of subcooling will be higher
Discharge pressure will be lower, subcooling will be higher
The discharge pressure will be lower, and the subcooling will be lower

111

Difficult

What is the benefit of using helium as a tracer gas in nitrogen during a pressure test?


It has smaller molecules and diffuses more easily
It has a higher pressure than pure nitrogen
It is non-flammable
It has a distinct odour

112

Difficult

Why should an R744 system that has been drained be initially charged with the refrigerant in gaseous form?


To prevent the drain valve from opening
To prevent damage to the compressor
To ensure that R744 is charged slowly
To prevent the formation of dry ice

113

Difficult

If an R744 system contains moisture because it has not been properly drained, what is the likely consequence?


Excessively high discharge pressure
The formation of hydrogen fluoride, which will decompose into hydrofluoric acid and damage the compressor
Reduced cooling capacity
The formation of carbonic acid, which will cause damage to the system

114

Difficult

Which system may require manual oil recovery?


Supercritical ‘booster’ system using R744
R744 cascade system
An R717 system
Secondary system using R744

115

Difficult

The pressure of R744 at a saturation temperature of 20 °C is approx.


25 bar g
90 bar g
56 bar g
14 bar g

116

Difficult

Which refrigerant is lighter than air?


R1234ze
R1270
R744
R717

117

Difficult

What hazards are associated with a Class A3 safety agent?


Lower toxicity, does not propagate flames
High toxicity, does not propagate flames
High flammability, lower toxicity
Slightly flammable, lower toxicity

118

Difficult

18 What is the GWP of R32 (according to AR4)?


6
3945
0
675

119

Difficult

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, height of the indoor unit, floor area
Lower flammability limit, height of the indoor unit, floor area
Practical limit, room volume
Lower flammability limit, room volume

120

Difficult

What compressor displacement is required for R1270, relative to R404A compressors for the medium-temperature range (cold store)?


Similar
50%
150%
600%

121

Difficult

At an ambient temperature of 25°C, the standby pressure in the low-pressure stage of an R744 cascade system will typically be…


Higher than the maximum permissible pressure in the low-pressure stage
The same as the pressure set on the relief valve
27.5 bar g
The same as the high-pressure setting on the pressure switch

122

Difficult

What is the correct definition of critical temperature?


The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature at which, for certain substances, electrical resistance is zero
The temperature above which there are no distinct liquid and gaseous phases
The temperature at which a substance changes from a gaseous to a solid state

123

Difficult

In a supercritical system, under supercritical conditions, the working fluid in the gas cooler


loses heat during a phase change
it loses heat when its pressure drops
loses heat at constant temperature and pressure
it loses heat as its temperature drops

124

Difficult

R717 is highly corrosive to


stainless steel
copper
aluminium
titanium

125

Difficult

What is the effect of repeatedly opening the relief valve?


The relief pressure drops
The relief pressure rises
The valve remains fully open continuously
The valve will not open

126

Difficult

What is the relationship between the pressure (P) and temperature (T) of nitrogen at the start (1) and end (2) of the leak test?


P2 = (P1 × T2)/T1
P2 = T1/(P1 × T2)
P2 = (P1 × T1)/T2
P2 = T2/(P1 × T1)

127

Difficult

What is the recommended alarm level for fixed leak detection systems for R717?


5,000 ppm
500,000 ppm
500 ppm
50,000 ppm

128

Difficult

Why are compressors with a separate electric motor most commonly used in R717 (NH₃) refrigeration systems?


To reduce the condensing pressure
To increase the amount of refrigerant in the system
Because NH₃ reacts with the motor windings and hermetic compressors are not used
Because compressors with a separate motor are cheaper

129

Difficult

Which type of compressor is most commonly used in large ammonia systems?


A reciprocating or screw compressor
Hermetic scroll
Rotary vane compressor
Diaphragm compressor

130

Difficult

How is the capacity of a piston compressor regulated in NH₃ systems?


By increasing the condensing pressure
By unloading the cylinders or changing the rotational speed
By reducing the refrigerant charge
Solely by adjusting the oil volume

131

Difficult

How is the capacity of a screw compressor most commonly controlled?


By using a slide valve
By changing the type of oil
By closing the suction valve
By adjusting the oil level

132

Difficult

When is two-stage compression used in NH₃ systems?


Only with water-cooled condensers
At small temperature differences
At very low vapour pressures and high pressure differentials
Exclusively in small systems

133

Difficult

What is the advantage of two-stage compression over single-stage compression?


Higher efficiency and lower discharge temperature
Lower efficiency
No need for a separator
Higher energy consumption

134

Difficult

How does an evaporative condenser used in NH₃ systems work?


It does not require a water supply
It transfers heat only to the air
It utilises the evaporation of water to increase cooling efficiency
Operates without a fan

135

Difficult

What is the function of the liquid separator in an NH₃ system?


It prevents liquid from entering the compressor
Regulates the condensing pressure
Increases the discharge temperature
It separates oil from the refrigerant

136

Difficult

What is the purpose of monitoring the liquid level in the separator?


To increase the oil volume
To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To reduce the condensing temperature

137

Difficult

What is the role of the float switch in NH₃ systems?


It monitors the liquid level in the tank or separator
It is used to detect leaks
It controls the fan’s operation
It regulates the condensation temperature

138

Difficult

What is a thermosiphon in NH₃ systems?


An oil circulation system utilising differences in pressure and temperature
A type of safety valve
A defrosting device
A type of evaporator

139

Difficult

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
Because NH₃ does not mix with most compressor oils
To increase the amount of refrigerant
Because the oil mixes only with water

140

Difficult

What is the main function of an oil separator in NH₃ systems?


To separate the oil from the refrigerant and return the oil to the compressor
Removing moisture from the system
To lower the condensation temperature
To increase fan efficiency

141

Difficult

Which NH₃ system features direct evaporation of the refrigerant in the evaporator?


Indirect system
Glycol system
Thermosiphon system
Direct expansion (DX) system

142

Difficult

What is the characteristic feature of a flooded evaporator system?


The evaporator is filled exclusively with vapour
The evaporator contains a large amount of liquid, which improves heat transfer
No level control is required
No separator is used

143

Difficult

What is the main difference between a direct and an indirect system?


In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In an indirect system, NH₃ flows directly into the space being cooled
In a direct system, there is no evaporator

144

Difficult

Which parts of refrigeration systems must be inspected on a mandatory and regular basis in accordance with EU Regulation 1516/2007?


Connections on the condenser, as there is high pressure and the refrigerant is in liquid form
Only compressor connections, as these are subject to vibration.
Fittings, 2. valves, 3. seals, 4. parts/components exposed to vibration, 5. connections at safety devices.
Compressor connections, 2. connections on the liquid refrigerant tank

145

Difficult

In accordance with EU Regulation 1516/2007, there are several methods of leak testing. What are these methods called?


We distinguish between quality control methods for supplied materials and electronic testing methods.
We distinguish between physical and chemical methods.
We distinguish between direct and indirect methods of leak detection.
We distinguish between methods for quality control of supplied materials and leak testing methods that do not involve quality control of supplied materials.

146

Difficult

In accordance with EU Regulation 1516/2007, to whom can we entrust the responsibilities for leak testing of refrigeration systems?


The inspection may be carried out by a person employed and appointed by the owner of the installation.
The test may only be carried out by a competent person with the relevant skills, who holds a certificate attesting to the necessary knowledge in this field. They must also hold a certificate for companies regarding the operation and maintenance of refrigeration equipment charged with F-gases.
The check may be carried out by a specialist in leak testing.
The check may only be carried out by a person who has previously carried out such a check.

147

Difficult

In accordance with EU Regulation 1516/2007, what conditions must be met in order to carry out a leak test on refrigeration systems using ultraviolet (UV) light?


A prerequisite for carrying out the inspection is holding the relevant authorisation for pressure testing issued by the UDT.
A prerequisite for carrying out a leak test using UV is that such a test is technically feasible.
The manufacturer of the refrigeration equipment must confirm that the aforementioned UV method can be used. A UV leak test may be carried out by a qualified person who holds the relevant qualifications (certificate).
A prerequisite for carrying out a leak test using UV is having the appropriate technical resources, the relevant materials supplied, and suitable safety goggles.

148

Difficult

In accordance with EU Regulation 1516/2007, which leak testing methods are classified as direct leak testing methods?


Leak test using nitrogen with a tracer gas, an electronic detector and pressure measurement.
Leak test following the creation of a vacuum and leak detection using a foaming solution.
Detection of leaks using a handheld leak detector and/or a fixed leak detection system; 2. Detection of leaks using a special dye with UV-fluorescent properties; 3. Detection of leaks using a foaming solution.
Leak testing by measuring pressure changes and the method of submerging the device/system in water.

149

Difficult

In accordance with EU Regulation 1516/2007, which methods are classified as indirect leak testing methods?


This method is based on electronic leak detection.
It utilises pressure and temperature measurements, as well as an ultrasonic method.
Leak detection using a UV tracer.
This method is based on the analysis of the following parameters: pressure, temperature, operating pressure, liquid level, oil leakage, etc.

150

Difficult

What does a vacuum leak test involve?


After switching off the vacuum pump, we check whether the pressure in the system rises
If the pressure in the refrigeration system were to rise, we switch on the vacuum pump as required.
With the vacuum pump running continuously, we are able to maintain the required vacuum level in the system.
With the vacuum pump switched on, check whether the pressure in the system rises as a result of a leak.

151

Difficult

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


On initial commissioning.
At least once every 12 months.
Once every six months.
Only when servicing the unit.

152

Difficult

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Only when servicing the unit.
Once every six months.
On initial commissioning.
At least once every 12 months.

153

Difficult

In accordance with Regulation (EU) 2024/573 of the European Parliament and of the Council, a fixed leak detection system is required when:


The installation of a fixed leak detection system is optional, but it helps to reduce the number of leak checks required on the equipment each year.
The charge of an F-gas refrigerant in a refrigeration unit is at least 500 tonnes of CO₂ equivalent.
The refrigeration equipment is operated in an enclosed space.
The refrigerant charge of the refrigeration equipment is at least 100 kg of ODS.

154

Difficult

Under Regulation (EC) No 1516/2007 and the F-gas Act, which leak detection methods may not be carried out by a person holding a Category E certificate?


Leak detection using a foaming solution.
Measuring leaks using a handheld leak detector.
Leak testing using a fluorescent dye.
Visual leak inspection.

155

Difficult

According to the current regulation, what sensitivity must a handheld leak detector have?


5 g/year.
10 g/year.
3 g/year.
8 g/year.

156

Difficult

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At any time.
Immediately after the repair.
At the next periodic inspection.
Between 24 hours and 1 month after the repair.

157

Difficult

At what intervals should leak tests be carried out on refrigeration equipment containing more than 500 tonnes of CO₂ equivalent of fluorinated greenhouse gases that does not have a leak detection system installed?


Once every 12 months.
Once every 6 months.
Once a month.
Once every 3 months.