F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Easy


2

Easy

What is the base unit of mass in the International System of Units (SI)?


N
kg
lb (pound)
t

3

Medium

What process takes place in the condenser of a refrigeration system?


Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled
The refrigerant absorbs heat from the surroundings and evaporates
The refrigerant rejects only the heat generated in the compressor
The secondary fluid (glycol, water) condenses while the refrigerant evaporates

4

Medium

What mainly determines the condensing temperature of an air-cooled condenser?


The evaporating temperature
The ambient (inlet) air temperature
The superheat
The compressor discharge temperature

5

Medium

Why does heat flow from the condenser to the surroundings?


Because the compressor pushes heat directly into the surroundings
Because the pressure in the condenser is lower than ambient
Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics)
Because HFC refrigerants attract heat from the surroundings

6

Medium

What should you mainly pay attention to when operating a condenser?


That the inlet air temperature is lower than the outlet air temperature
Its general condition and the cleanliness of the heat-exchange surfaces
The colour of the condenser casing
That the outlet air temperature is higher than the condensing temperature

7

Medium

What criteria should be considered when selecting a suitable condenser?


Only the size and number of fans
Fan noise, connection diameters and colour
Only own experience and the dimensions
The required capacity of the condenser and the technical specifications declared by the manufacturer

8

Medium

How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?


Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers.
Contaminants increase the heat transfer area and reduce the condensing pressure.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency.

9

Medium

How does the capacity of an air-cooled condenser change when it becomes dirty?


It remains unchanged
It decreases
It increases because the fan speed rises
It increases

10

Medium

What is the main consequence of heavy frost on an air-cooling evaporator?


A rise in the cooled-air temperature with no effect on capacity
Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature
A rise in evaporating pressure
An increase in condenser subcooling

11

Medium

What happens when the evaporation temperature drops?


The compressor’s cooling capacity increases.
The compressor’s cooling capacity decreases.
The discharge temperature decreases.
The condenser fan speed increases.

12

Medium

When is natural (off-cycle, air) defrosting possible?


Only in freezer rooms below −18 °C
Only in coolers fitted with speed-controlled fans
When the air passing through the cooler is above 0 °C
Never – electric heaters must be used in every air cooler

13

Medium

When does frost form on the surface of an air-cooling evaporator?


Only when the system runs continuously
When the evaporator surface temperature is below 0 °C and below the dew point of the air
Only when the room air temperature falls below 0 °C
Always, in every air cooler

14

Medium

In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…


…insulating the discharge line between the compressor and the condenser
…using smaller-diameter pipes
…increasing the length of the liquid line
…additional subcooling of the liquid

15

Medium

How does hot gas defrosting of the evaporator work?


We swap the outlet and inlet sides of the evaporator.
Heated vapour (hot gas) from the compressor is directed into the evaporator piping.
This involves reversing the direction of rotation of the compressor.
We switch on the gas heater directed at the evaporator.

16

Medium

What is the function of the evaporator in a refrigeration system?


It ensures that the refrigerant is superheated over the largest possible heat exchange surface area.
It evaporates the water flowing through the evaporator.
It cools the refrigerant.
It transfers heat from the medium being cooled to the boiling refrigerant.

17

Medium

What condition must electric heaters for evaporator defrosting meet?


Heat from the heaters must be carried by the running fans
They must be in direct contact with the refrigerant
They must be located beneath the evaporator
They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block)

18

Medium

Refrigerant distributor:


ensures even distribution of the refrigerant to the individual sections of the condenser.
ensures the even distribution of the refrigerant discharged by compressors connected in parallel.
acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded.
ensures an even distribution of the refrigerant to the individual sections of the evaporator.

19

Medium

What defrosting methods are used for air coolers?


Electric, hot gas, water spray and natural (at positive temperatures)
Only by switching off the fans with the compressor running
Electric only – other methods are not permitted in refrigeration
Natural only – other methods are ineffective and uneconomic

20

Medium

The boiling point of a liquid rises when the pressure above the liquid…


…varies depending on the ambient temperature
…falls
…remains constant
…rises

21

Medium

MOP in thermostatic expansion valves stands for:


maximum operating pressure.
maximum pressure switch protection.
self-cleaning of the valve in the event of moisture in the refrigerant freezing.
minimum flow opening.

22

Medium

The function of a thermostatic expansion valve (TEV) is:


to maintain a constant condensing pressure
to adjust the evaporating pressure in the condenser
to maintain a constant compressor suction pressure
to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator

23

Medium

What type of compressor motor can be used with a capillary tube?


A low-speed motor
A low-starting-torque motor (pressures equalise during standstill)
A high-starting-torque motor must be used
An electronically commutated motor

24

Medium

What does a thermostatic expansion valve control?


The temperature in the cold room
The discharge temperature
The condensing pressure
The mass flow of refrigerant fed into the evaporator

25

Easy

The refrigerant absorbs heat when…


…it freezes
…it evaporates
…it is subcooled
…it condenses

26

Medium

What does the manufacturer state as the factory setting of a thermostatic expansion valve?


the degree of refrigerant expansion.
the superheat value during valve operation.
the static superheat of the valve.
the degree to which the valve is filled with refrigerant liquid.

27

Medium

Where is a new or repaired system with an expansion valve and liquid receiver charged?


In the liquid phase into the compressor suction, with the compressor running
In the liquid phase on the high-pressure side, with the compressor stopped
Anywhere – the charging point does not matter
Through the capillary tube outlet during normal system operation

28

Medium

What does a thermostatic or electronic expansion valve control?


The amount of refrigerant fed to the evaporator according to superheat
The evaporating pressure – closing below the set point
Subcooling, by adjusting condensing pressure
The compressor speed

29

Medium

What does the MOP function of thermostatic expansion valves mean?


The valve limits subcooling
The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost
The valve maintains a constant condensing pressure
The valve prevents motor overheating by injecting liquid into the compressor

30

Medium

The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…


…the lower qo, with Qo unchanged
…the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo
…the lower qo and the lower energy efficiency
…the lower qo and the lower Qo

31

Medium

How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?


Higher by approx. 20 K
Freely – the MOP value is irrelevant
A few kelvin higher (approximately 7 K)
About 7 K lower than that temperature

32

Medium

What is the function of the suction pressure regulator?


It maintains the evaporation pressure at a constant level.
It limits the suction pressure and protects the compressor from excessively high suction pressure.
It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system.
To maintain the suction pressure at the highest possible level.

33

Medium

What is the function of the valve regulating water flow through the condenser?


To maintain the condensing pressure at the highest possible level.
To maintain the condensing pressure at a constant level.
To maintain the water temperature at the highest level.
To maintain the condensing pressure at the lowest possible level.

34

Medium

The use of a refrigerant distributor requires a thermostatic expansion valve ...


... with an adsorption-type sensor filling.
... with internal pressure equalisation.
... with external pressure equalisation.
... with a MOP function.

35

Medium

What properties should good insulation materials have?


An antistatic coating
The ability to absorb large amounts of moisture
High thermal conductivity
Low thermal conductivity (and low water absorption, vapour tightness)

36

Medium

When is refrigerant vapour superheated?


When its temperature is higher than the saturation temperature corresponding to its pressure
When the compressor motor temperature rises excessively
When the pressure on the discharge side is higher than on the suction side
When the evaporating temperature is lower than the ambient temperature

37

Medium

How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?


We check using a pressure gauge fitted on the discharge side of the compressor.
We are unable to check this.
We check using a liquid pressure gauge.
We check this using a sight glass.

38

Medium

Where does the liquid line run?


Between the evaporator and the compressor
Between the evaporator and the suction-line heat exchanger
Between the compressor and the condenser
From the condenser (liquid receiver) to the expansion valve

39

Medium

What is the function of the liquid receiver in a refrigeration system?


To store refrigerant and compensate for changes in the circulating charge as the heat load varies
To collect liquid refrigerant and excess oil
To further subcool the condensed refrigerant
To act as a reserve when the required charge is unknown

40

Medium

What is the purpose of the liquid receiver during service work?


It further subcools the refrigerant before the expansion valve
It is a reserve when the installer does not know the required charge
It collects excess oil circulating in the system
It allows pump-down and temporary storage of the refrigerant

41

Medium

Where should the liquid receiver be installed?


It should be installed downstream of the condenser, upstream of the expansion valve.
It should be fitted between the compressor and the condenser.
It should be fitted after the evaporator.
It should be fitted just before the compressor.

42

Medium

What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?


It closes when the suction pressure upstream of the compressor drops.
It opens when the suction pressure upstream of the compressor drops.
It regulates the condensing pressure.
It regulates the evaporation pressure.

43

Medium

The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:


A reduction in the system’s energy efficiency.
There is no effect whatsoever on either the amount of refrigerant or energy efficiency.
An increase in the amount of refrigerant in the system and an increase in condensing pressure.
A reduction in refrigerant charge and, typically, higher energy efficiency.

44

Medium

Which refrigerants belong to the HFC group?


R134a, R404A, R507A, R410A.
R11, R12, R502.
R134a, R32, R22, R507A, R290.
R22, R401A.

45

Medium

Which refrigerants belong to the HFO group?


R134a, R404A.
R1234yf, R1234ze(E).
R22, R12.
R134a, R290.

46

Medium

What are the characteristics of R410A refrigerant compared to R407C refrigerant?


The saturation pressure of R407C is 150% higher than that of R410A.
The saturation pressure of R410A refrigerant is higher than that of R407C.
The saturation pressure of both refrigerants is roughly the same.
The saturation pressure of R407C refrigerant is much higher than that of R410A.

47

Medium

What does the TEWI indicator define?


Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime
The impact of a refrigerant on the ozone layer
The global warming potential of a gas relative to CO₂ over a 100-year horizon
The ability of the ozone layer to recover

48

Medium

What are the characteristics of R452A compared with R404A?


Both are azeotropic and have no temperature glide
It is a flammable and toxic single-component HFC
It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower
The temperature glide of R452A is half that of R404A

49

Medium

What distinguishes R1234yf from R134a?


It is mildly flammable (class A2L), whereas R134a is non-flammable (A1)
A higher critical temperature
A higher normal boiling point
Higher toxicity

50

Medium

How does CO₂ (R744) compare with R134a?


Its temperature glide is 7 K greater than that of R134a
It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes)
It has identical properties and is a drop-in replacement for R134a
Unlike R134a, it is an azeotropic mixture

51

Medium

Which of the following is NOT a fluorinated greenhouse gas?


Perfluorocarbons (PFCs).
Sulphur hexafluoride (SF6).
Hydrofluorocarbons (HFCs).
Carbon dioxide (CO₂).

52

Difficult

What additional protective equipment will you use when brazing systems containing HC refrigerants?


Ear defenders
A high-visibility vest
Latex gloves
A flammable gas detector

53

Difficult

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


The pressure switch setting will not be correct
It is a potential source of ignition
Dust and moisture may enter
There is a risk of refrigerant leakage

54

Difficult

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


3 m
1 m
0.5 m
2 m

55

Difficult

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


20 kg
33 kg
9 kg
18 kg

56

Difficult

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


2.5 kg
10 kg
0,494 kg
1.0 kg

57

Difficult

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Place the pump directly on the floor, as low as possible
Such systems need not be evacuated before charging
Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level

58

Medium

What is the greenhouse effect?


Clouds reflect ultraviolet radiation, which makes the air near the surface warmer
Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere
Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface
Dust in the atmosphere reflects sunlight, lowering the average surface temperature

59

Difficult

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


Thick gloves
A fire blanket
A fire extinguisher
Tinted safety goggles

60

Difficult

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Vent the R32 outdoors and purge the system
Recover the R32 to a vacuum and start desoldering immediately
Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Vent the R32 outdoors, then fill and vent the system with nitrogen three times

61

Medium

What is R1270?


n-Butane
Propene (propylene)
Isobutane
Propane

62

Difficult

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Leak detection foam
Electronic leak detector for flammable refrigerants
Electronic HFC leak detector
Soapy water solution

63

Difficult

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


A different colour for the station
A flammable refrigerant recovery unit has no ignition sources
Different connection sizes
Different low-pressure switch setting

64

Difficult

Which of the following is a source of ignition?


An 'n'-type (non-sparking) thermostat
A sealed NTC temperature sensor
A contactor (sparking contacts)
An Ex-certified fan motor

65

Difficult

What particularly hazardous substance is formed when R32 burns?


Phosgene
Sulphur dioxide (SO₂)
Hydrogen fluoride (HF)
Hydrogen chloride (HCl)

66

Difficult

What type of refrigerant is R1234ze(E)?


CFC (chlorofluorocarbon)
HCFC (hydrochlorofluorocarbon)
HC (hydrocarbon)
HFO (hydrofluoroolefin)

67

Difficult

What hazards does a safety group A3 refrigerant pose?


Higher toxicity, moderate flammability
Lower toxicity, higher flammability
Lower toxicity, moderate flammability
Higher toxicity, higher flammability

68

Difficult

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.5 kg
1.0 kg
0.285 kg
4.93 kg

69

Easy

What does the GWP indicator mean?


The annual rise in mean air temperature caused by the emission of 1 kg of the gas
Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
Ozone depletion potential
The ability of a substance to restore the ozone layer

70

Difficult

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.75
approx. 0.6
approx. 1.05–1.1
approx. 1.3

71

Difficult

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they must be kept running continuously to disperse the leaking refrigerant
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they are more energy-efficient
Because they are more reliable

72

Difficult

Why is the density difference between HC and HFC refrigerants important?


Because HCs operate at much higher pressures
An HC charge in kg is roughly half that of an HFC
Because it determines the system's energy efficiency
Because HCs must be charged much more slowly than HFCs

73

Difficult

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


150
675
0.02
7

74

Difficult

Which of the following is NOT a source of ignition?


An unsealed mechanical pressure switch
An Ex-certified fan motor
A light switch
An electrical switch

75

Difficult

What is R290?


Propene (Propylene)
Butane
Propane
Isobutane

76

Difficult

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


1.2 kg
150 g
2.5 kg
1.5 kg

77

Difficult

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


It could be a source of ignition
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
A relay is never required for compressors using flammable refrigerants
The method of starting the compressor motor differs from that used with HFCs

78

Difficult

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


10 m
5 m
3 m
1 m

79

Difficult

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


approx. 17 kg
approx. 8 kg
approx. 5.2 kg
20 kg

80

Medium

How do refrigeration systems contribute to the greenhouse effect?


Through oil emitted into the atmosphere from the condenser and filter
Only through CO₂ given off by the compressor motor
Only through the heat rejected by the condenser
Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere)

81

Difficult

How can a vacuum pump be used safely to evacuate a system containing R290?


Ignition-source-free pump, good ventilation, exhaust to a safe place
R290 systems need not be evacuated before charging
Place the pump directly on the floor, as low as possible
Position the pump at least 3 m above floor level

82

Difficult

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


Tinted safety goggles
Thick gloves
A fire blanket
A fire extinguisher (at least 2 kg dry powder)

83

Difficult

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Purge the system with compressed air
Ensure good ventilation and check the work area with a flammable gas detector
Working outdoors is sufficient
Such joints must never be desoldered; they must be cut with a pipe cutter

84

Difficult

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 into the room and open a window
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Vent the R1270 outdoors and start brazing immediately

85

Difficult

Which method should NOT be used to locate an R290 leak?


Leak detection foam
An electronic detector for flammable refrigerants
Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic leak detector designed for HFCs

86

Difficult

Why can’t recovery stations designed for HFCs be used with R600a?


The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
They contain ignition sources
The oil in the recovery unit is not soluble in R600a
The recovery unit cannot withstand the working pressure of R600a

87

Difficult

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


227 kg
2.27 kg
6.18 kg
618 kg

88

Difficult

What type of refrigerant is R32?


Hydrofluoroolefin
Hydrocarbon
Hydrofluorocarbon
Carbon dioxide

89

Difficult

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Lower toxicity, higher flammability
Higher toxicity, lower flammability
Higher toxicity, higher flammability

90

Difficult

What hazard is associated with the combustion of HFO or HFC refrigerants?


Ozone is formed
Phosgene is formed
Hydrogen fluoride (HF) is formed
Nitrous oxide is formed

91

Medium

What is the greenhouse effect?


The absorption of solar radiation by the Earth's surface
The formation of a layer that traps only heat from fuel combustion in aircraft
The filtering of solar radiation by the atmosphere
The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space

92

Difficult

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About half
About seven times as large
About twice as large
The same

93

Difficult

What is the GWP value for R32 according to Regulation (EU) 2024/573?


0
675
3
7

94

Difficult

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because such systems never have liquid receivers
Because R290 is only used in systems below 150 g
Because of lower operating pressures

95

Difficult

Why does the condenser fan run continuously in some systems using R1270?


To ensure that the discharge pressure never becomes excessive
To dilute the refrigerant in the event of a leak
To prevent the build-up of contaminants in the condenser
To reduce energy consumption

96

Medium

Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?


Regulation (EU) No 517/2014
Regulation (EU) 2024/573
Directive 2009/125/EC
Regulation (EU) 2015/1188

97

Medium

What is the main objective of Regulation (EU) 2024/573?


To reduce taxes on refrigeration equipment
Standardising metal recycling standards
To facilitate the import of electrical appliances
Prevention of F-gas emissions and the achievement of the EU’s climate targets

98

Medium

What are the ecodesign obligations of manufacturers of refrigerating appliances?


Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability
Only implementing an ISO 9001 quality management system
Only using energy labels under Regulation (EU) 2024/573
Only declaring F-gas quantities under Regulation (EU) No 517/2014

99

Medium

What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?


To facilitate imports from outside the EU
To increase sales of electrical appliances in the EU
To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability
To standardise the appearance of products in the EU

100

Medium

What is the function of a ball valve in a refrigeration system?


Enables the refrigerant flow to be completely shut off
It prevents excessive pressure build-up in the system
It regulates the temperature of the refrigerant
It measures the moisture content of the refrigerant

101

Easy

What is the main function of a safety valve?


Prevents the evaporator from freezing
It monitors the moisture content of the refrigerant
Discharges refrigerant when the set pressure is exceeded
It controls the oil level in the compressor

102

Medium

How do certain gases contribute to the greenhouse effect?


They deplete the ozone layer, so more solar radiation reaches the surface
They trap thermal radiation that the Earth would otherwise emit into space
They limit UV radiation reaching the Earth's surface, changing the heat balance
They heat the air through chemical reactions with atmospheric oxygen and nitrogen

103

Medium

What is the purpose of a sight glass (with moisture indicator)?


Measuring condenser temperature
Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture
Emergency shut-off of flow
Regulating compressor pressure

104

Medium

What is the function of the temperature regulator in a refrigeration system?


It drains excess refrigerant into the receiver
To maintain a constant pressure in the compressor
Controls the operation of the compressor and valves to maintain the set temperature
It restricts oil flow

105

Difficult

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It prevents liquid refrigerant from entering the compressor
It separates liquid from oil
It heats the refrigerant before the evaporator
It is used only to measure moisture

106

Difficult

What is the function of an oil separator in systems using flammable or toxic refrigerants?


They are used solely to measure the moisture content of the refrigerant
Heats the refrigerant before it enters the evaporator
Separates oil from the refrigerant and facilitates the return of oil to the compressor
It prevents liquid from entering the compressor

107

Medium

What is the purpose of oil level regulators in a refrigeration system?


They control the pressure in the condenser
Maintains the correct oil level in the compressor
They drain off excess refrigerant
They control the evaporator temperature

108

Medium

What is the function of the liquid receiver in relation to system tightness?


It controls the evaporating temperature by varying the circulating charge
It stores refrigerant; checking its liquid level helps detect charge loss
It regulates the oil returning to the compressor
It keeps the whole system at constant pressure regardless of load

109

Medium

What is the role of a gauge manifold with thermometers (temperature probes)?


It relieves pressure if it is exceeded
It controls oil level
It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check)
It monitors refrigerant moisture content

110

Medium

What is the role of defrost controls?


They drain excess oil from the evaporator to the receiver
They protect the evaporator from icing and damage that could lead to leaks
They monitor the moisture content of the refrigerant
They control compressor discharge pressure during defrost

111

Difficult

Why do liquid and oil separators in CO₂ systems require particular attention?


Because CO₂ needs no lubrication, so oil separators are unnecessary
Because sight glasses and level indicators must not be used in CO₂ systems
Because of very high pressures – adequate PS and protection devices are required
Because CO₂ is flammable and separators must not be used

112

Difficult

What is the critical pressure of CO₂ (R744)?


Approx. 74 bar (abs)
Approx. 10 bar
Approx. 31 bar
Approx. 120 bar

113

Easy

What is the unit of pressure in the International System of Units (SI)?


bar (gauge)
Pa (pascal)
atm (standard atmosphere)
psi (pound per square inch)

114

Medium

Where can the lists of fluorinated greenhouse gases be found?


In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In the Vienna Convention for the Protection of the Ozone Layer
In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases
In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council

115

Difficult

What characterises the transcritical process in CO₂ systems?


Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
It is irrelevant to system operation
Conventional condensation occurs
It occurs only at low temperatures

116

Difficult

What characterises the subcritical CO₂ process?


The absence of condensation
The absence of evaporation
The conventional condensation process below the critical point
Operation above the critical point

117

Easy

What is the log(p)-h diagram for CO₂ used for?


To measure temperature
For analysing thermodynamic processes in a refrigeration system
To regulate pressure
To detect leaks

118

Easy

What can be read from the log(p)-h graph?


Only the temperature
Only the amount of refrigerant
Only the humidity
Pressure, enthalpy, temperature and state of the refrigerant

119

Easy

What are CO₂ saturation tables used for?


To determine the relationship between temperature and pressure at saturation
To measure humidity
To determine the oil quantity
To regulate the compressor

120

Easy

What does the CO₂ saturation state mean?


Dry ice state
A state of high pressure
A state in which the refrigerant is only a gas
Equilibrium between the liquid and vapour phases

121

Difficult

When can dry ice (solid CO₂) form?


When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system
At high temperature
During normal operation of the system
At high pressure

122

Difficult

What risks are associated with dry ice forming in a CO₂ system?


Pressure reduction
Improved efficiency
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
No risk

123

Difficult

How does CO₂ saturation pressure change as temperature increases?


It first decreases, then increases
It remains the same
It increases rapidly
It decreases

124

Easy

Why is understanding the log(p)-h graph particularly important for CO₂?


It is only used for design purposes
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It only applies to NH₃
It doesn’t matter

125

Medium

Where can the lists of ozone-depleting substances be found?


In the Vienna Convention for the Protection of the Ozone Layer
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In a regulation of the Minister of the Environment on the list of controlled substances
In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council

126

Difficult

What happens to CO₂ above the critical point?


It ceases to conduct heat
It turns into a solid
It turns into a liquid
It transitions to a supercritical state (no distinction between liquid and gas)

127

Easy

Why do CO₂ systems require precise pressure control?


Because there are no valves
Due to significant pressure changes with temperature fluctuations
They do not require control
Due to low pressures

128

Medium

Why is ammonia (R717) classed as a toxic refrigerant?


It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations
Because it is colourless and odourless and therefore hard to detect
Because it does not react with water, making neutralisation difficult
Because it is heavier than air and displaces oxygen

129

Difficult

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator always has a lower pressure than a flooded one
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)

130

Difficult

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Below atmospheric (approx. 0.7 bar abs at −40 °C)
Atmospheric pressure, approx. 1 bar abs
Positive pressure of 5–10 bar
Positive pressure of 10–20 bar

131

Difficult

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are readily biodegradable
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They cause rapid cooling of the atmosphere
They are climate- and environment-neutral

132

Easy

What is the basic requirement when charging a system with R717 (NH₃)?


Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment
NH₃ can be charged together with air
Charging should take place in a well-ventilated area using appropriate personal protective equipment

133

Difficult

How is oil managed in R717 systems?


Oil can be mixed with any refrigerant
Oil requires no monitoring
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil has no effect on system operation

134

Easy

What is the correct procedure for recovering R717 from a system?


The refrigerant can be drained into the sewer system
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
Recovery is not required
The gas can be released into the atmosphere

135

Easy

How should R717 (NH₃) be stored?


In any open containers
In unmarked plastic containers
In sealed, labelled containers, in a cool and well-ventilated place
Near heat sources

136

Medium

Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?


By 31 January, in the Central Register of Operators (CRO)
By 31 March, electronically to the Ministry of Climate and Environment
By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP)
By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT)

137

Difficult

What should be done with contaminated R717?


Release it into the atmosphere
Purify it or send it for disposal in accordance with regulations
Continue to use it without restriction
Dilute it with water and reuse it

138

Easy

What is the main hazard associated with an R717 leak during maintenance work?


Damage to electrical equipment only
Increased cooling efficiency
Toxic to humans and may cause chemical burns
No risk whatsoever

139

Difficult

What should be done if an NH₃ leak is detected?


Carry on working with the room door open
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Carry on working wearing a dust mask
Increase the pressure in the system

140

Difficult

What role do scrubbers play in NH₃ systems?


Neutralise ammonia through absorption in a liquid (e.g. water)
They increase the pressure in the system
They store the refrigerant
They are used to measure temperature

141

Difficult

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level
Simply start it up
There is no need to check it

142

Difficult

What are the transport requirements for R717?


It can be carried in open containers
It can be carried without labelling
Transport is not regulated
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)

143

Easy

What personal protective equipment is required when working with NH₃?


Workwear only
Only a safety helmet
No requirements
Safety goggles, gloves and respiratory protective equipment

144

Medium

Which installation measure has a major impact on compressor energy efficiency?


Proper evacuation and dehydration of the system (removing air and moisture)
Omitting the filter-drier to reduce flow resistance
Charging extra refrigerant 'as a reserve' above the nameplate value
Installing a suction line smaller than recommended

145

Medium

How does regular oil-level monitoring affect compressor operation?


It allows any type of oil to be topped up
It allows the crankcase heater to be omitted
It increases cooling capacity above nominal
It ensures proper lubrication and limits wear and energy losses

146

Easy

How do system leaks affect compressor energy efficiency?


No effect as long as the system still cools
They improve efficiency because condensing pressure drops
They affect only safety, not energy use
Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)

147

Medium

Regulation (EU) 2024/590 relates to:


Health and safety during refrigerant recovery
Ozone-depleting substances
Alternative refrigerants replacing fluorinated greenhouse gases
Conditions for F-gas certification of companies recovering and reclaiming refrigerants

148

Medium

What is the significance of proper suction and discharge pressure control?


The highest possible condensing pressure is best
It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible)
The lowest possible suction pressure is best
Pressures do not affect energy use

149

Medium

Which maintenance measure reduces compressor energy consumption?


Raising the high-pressure switch setting
Topping up refrigerant at every service visit
Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary
Permanently disabling the crankcase heater

150

Medium

How does air (non-condensable gas) in the system affect operation?


It only affects the sight-glass indication
It raises the condensing pressure and reduces efficiency
It lowers the condensing pressure
It improves condenser heat transfer

151

Medium

What role do controls play in compressor efficiency?


They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching)
They increase the circulating refrigerant charge
They provide safety only, with no energy effect
They matter only in NH₃ systems

152

Medium

How does suction superheat at the compressor affect efficiency?


Excessive superheat reduces efficiency and raises the discharge temperature
Zero suction superheat is optimal
Superheat has no effect
The higher the superheat, the higher the efficiency

153

Medium

How does correct system layout affect efficiency?


It doesn't matter
It shortens pipe runs and limits pressure drops and energy losses
Longer pipes improve subcooling and always increase efficiency
It affects only appearance

154

Medium

How important is suction pipe insulation?


It increases energy consumption
It is needed only for appearance
It limits heat gain and excessive superheat, improving efficiency
It has no effect

155

Medium

Which measure most improves condenser energy efficiency?


Regular cleaning of heat-exchange surfaces
Raising the condensing pressure set point
Increasing the refrigerant charge
Reducing fan speed to the minimum

156

Easy

How does a dirty condenser affect the operation of the refrigeration system?


It improves efficiency
It lowers the condensing pressure
It has no effect
Causes an increase in pressure and energy consumption by the compressor

157

Easy

Why is adequate airflow through an air-cooled condenser important?


The lower the airflow, the lower the condensing pressure
It doesn't matter
It ensures effective heat rejection and low condensing pressure
It affects only noise

158

Medium

Which refrigerants damage the ozone layer?


All refrigerants containing carbon in their molecules
All refrigerants containing chlorine or bromine in their molecules
All natural refrigerants
All refrigerants containing fluorine and hydrogen in their molecules

159

Easy

How does the presence of limescale in a water-cooled condenser affect performance?


It improves heat transfer
It has no effect
It lowers the condensation temperature
Impairs heat exchange and increases energy consumption

160

Medium

How does correct condensing pressure control affect efficiency?


It has no effect
It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use
It always increases energy use
It is best to keep a constant high condensing pressure all year

161

Easy

How do condenser leaks affect energy efficiency?


Have no effect
They improve efficiency
They lower the temperature
Causes refrigerant loss and a drop in efficiency

162

Easy

How important is the correct positioning of an air-cooled condenser?


It should be installed in a well-ventilated area with unobstructed airflow
It should be housed in a small room
It doesn’t matter
It should be close to heat sources

163

Easy

How does hot air recirculation affect the condenser?


It improves efficiency
It reduces the pressure
Impairs cooling and increases energy consumption
It has no effect

164

Medium

How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?


It doesn't matter
It reduces energy losses and improves overall system efficiency
It impairs cooling
It increases pressure

165

Medium

Which measure most improves the energy efficiency of an air-cooling evaporator?


Increasing the refrigerant charge above nominal
Restricting the airflow through the evaporator
Raising the condensing temperature by a few kelvin
Defrosting at the right time and keeping the fins clean

166

Easy

How does evaporator icing affect the system’s operation?


It has no effect
It improves cooling performance
Impairs heat exchange and increases energy consumption
It lowers the condensation temperature

167

Easy

How does dirt on the evaporator surface affect its performance?


It improves efficiency
It has no effect
It reduces the pressure
Impairs heat exchange and increases energy consumption

168

Easy

What maintenance task is crucial for the evaporator?


Lack of maintenance
Increasing the refrigerant charge
Regular cleaning and defrosting
Reduced airflow

169

Medium

What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?


All activities involving equipment using CO₂ (R744)
All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems
Only leak checks that do not entail breaking into the refrigerant circuit
Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems)

170

Easy

How does superheat at the evaporator outlet affect efficiency?


It only causes a temperature drop
Excessive superheat reduces energy efficiency
It always improves performance
It has no effect

171

Easy

How do leaks in the evaporator affect efficiency?


Increase capacity
Improves performance
Have no effect
These cause refrigerant loss and a drop in efficiency

172

Easy

How important is correct expansion valve adjustment?


It doesn’t matter
It increases energy consumption
Causes leaks
Ensures optimal evaporator charge and improves efficiency

173

Easy

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It improves efficiency
It has no effect
It causes cooling losses and increased energy use
It lowers the condensing temperature

174

Easy

How does correct TEV adjustment affect system energy efficiency?


It has no effect
It ensures optimal superheat and improves efficiency
It causes leaks
It increases energy use

175

Easy

What happens if the superheat set by the TEV is too high?


It has no effect
Efficiency will drop because the evaporator is not being fully utilised
Cooling efficiency will improve
The refrigerant charge will increase

176

Medium

How does too low superheat setting on the TEV affect performance?


It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid
It has no effect
It increases operational safety
It reduces refrigerant flow

177

Easy

How do contaminants in the system affect the operation of the TEV?


They can cause it to become blocked and reduce efficiency
Have no effect
They lower the temperature
They improve its performance

178

Easy

What role does the filter-drier play in terms of system efficiency?


Removes moisture and contaminants, improving the system’s efficiency
It doesn’t matter
It lowers the temperature
It increases the amount of refrigerant

179

Easy

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


Prevents unwanted heat gains and improves efficiency
It doesn’t matter
It causes leaks
It increases energy consumption

180

Medium

What is the scope of Regulation (EU) 2024/573?


Design requirements and conformity assessment for pressure equipment
Only requirements for periodic leak checks of refrigeration equipment
Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting
Health and safety requirements for brazing and welding on refrigeration installations

181

Easy

How important is it to check the operation of the condensing pressure control valve in the system?


It increases energy consumption
It causes a significant rise in temperature
Ensures operation within the optimum pressure range and reduces energy losses
It has no effect

182

Easy

How does the correct selection of a TEV affect energy efficiency?


It lowers the temperature
It increases the amount of refrigerant
It doesn’t matter
Ensures the system is matched to its capacity and operates optimally

183

Medium

What is the main design difference in hydrocarbon refrigeration systems?


No need for safety measures
Higher operating pressures
The need to eliminate ignition sources and limit the charge because of the refrigerant's flammability
Lower energy efficiency

184

Medium

How do compressors used in hydrocarbon systems differ?


They need no lubrication
They must be approved by the manufacturer for the specific flammable refrigerant (e.g. electrical components that are not ignition sources, suitable oil)
They must operate at higher pressures than HFC compressors
There is no difference

185

Difficult

What is the main characteristic of R744 (CO₂) refrigeration systems?


No need for control
Very high operating pressures
Low energy efficiency under all conditions
Low operating pressures

186

Difficult

What are the requirements for piping materials in CO₂ systems?


It doesn't matter
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)
Any material may be used
Only plastics

187

Difficult

How does a booster system work in CO₂ installations?


It reduces evaporator pressure
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It is used to store refrigerant
It reduces the refrigerant quantity

188

Easy

What is the function of high-pressure control valves in CO₂ systems?


They lower the evaporator temperature
They are used to store the refrigerant
They regulate oil flow
They control the pressure on the high-pressure side and optimise system operation

189

Difficult

Why is pressure optimisation in CO₂ systems crucial?


It enables the system to achieve maximum energy efficiency in transcritical mode
It doesn’t matter
It reduces the amount of refrigerant
It reduces the ambient temperature

190

Difficult

What role does parallel compression play in CO₂ systems?


It lowers the ambient temperature
It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It has no significance
It increases energy consumption

191

Medium

How can you tell that the system has been overcharged with refrigerant?


The compressor runs at a lower load and the suction pressure drops
Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface
Even under a very small heat load, frost forms on the suction line
It cannot be checked, because the sight glass is not intended for this

192

Difficult

How does an ejector work in a CO₂ system?


It increases the amount of refrigerant
It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It lowers the evaporator temperature
Stores the refrigerant

193

Difficult

What is the function of liquid ejectors in CO₂ systems?


They reduce atmospheric pressure
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They raise the refrigerant temperature
They increase the amount of oil

194

Difficult

What are the characteristics of partially flooded systems in CO₂ systems?


Low operating pressure
Lack of regulation
The presence of liquid in the evaporator, which improves heat transfer and efficiency
The absence of liquid in the evaporator

195

Difficult

What is the main risk associated with standstill pressure in CO₂ systems?


A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
A drop in temperature
A decrease in refrigerant quantity
Increased efficiency

196

Difficult

How is standstill pressure limited in CO₂ systems?


By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By completely shutting down the system and power supply
By raising the plant-room temperature
By increasing the refrigerant charge

197

Difficult

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


Improved efficiency
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
A drop in system temperature
Normal system operation

198

Easy

Why do CO₂ systems require more advanced automation than traditional systems?


They do not require automation
Because there are no valves
Due to the need for precise control of pressure and temperature
Due to low pressures

199

Difficult

What must the label of a flammable refrigerant cylinder include?


The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Information about the cylinder owner
Only the refrigerant name
Only the net weight

200

Difficult

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It has no significant effect on safety
It reduces system efficiency
It may lead to the use of tools that are ignition sources
It may lead to the wrong oil being selected

201

Difficult

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Gross weight and batch number
Cylinder colour and date of manufacture
Manufacturer’s name and country of origin
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number

202

Medium

Before charging the unit with refrigerant, it is essential to…


…carry out a tightness test (and evacuate the system)
…fill in the unit's data sheet
…check the compressor suction and discharge connections
…carry out a trial start-up

203

Easy

What is the requirement regarding the labelling of an installation containing a flammable substance?


Colour-coding of pipes is sufficient
Labelling is required only in technical rooms
Labelling is not required for hermetically sealed systems
The labelling must indicate the type of substance and the flammability hazard

204

Easy

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


Risk of leakage and the formation of an explosive mixture
Merely installation difficulties
Merely a reduction in efficiency
No impact on safety

205

Difficult

What is the purpose of gas detectors in a room with a refrigeration system?


Monitoring pipe pressure
Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Measuring refrigerant temperature
Controlling compressor capacity

206

Difficult

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Once every 5 years
Only after a leak has occurred
Before every start-up of the unit

207

Difficult

Where should a gas detector be located according to EN 378?


Anywhere in the room
Only at the room entrance
Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Near the control panel

208

Easy

How should an employee respond when a gas alarm is triggered?


Switch off the system and wait for the alarm to stop
Carry on working until they see a leak
Reduce the pressure in the system
Leave the room immediately and notify their supervisor

209

Difficult

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


The colour of pipes and hoses
Only that the air filter is new
The presence of health and safety signage, adequate ventilation and gas detectors
Only the compressor power

210

Easy

Gas detectors should be installed in rooms where:


The amount of refrigerant exceeds a specified permissible threshold
Any refrigerant is present, regardless of the quantity
Ventilation is natural
The room is less than 5 m²

211

Difficult

What are the requirements for emergency exits from a refrigeration machinery room?


One exit with a sign stating the refrigerant type is sufficient
At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed
Outward-opening doors and signed escape routes (number of exits per the standard)

212

Difficult

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


A thorough tightness test and evacuation (dehydration) of the system
Omitting the filter-drier
Restricting room ventilation
Charging above the nameplate quantity

213

Medium

What information must appear on the label of equipment containing F-gases?


The manufacturer's logo, the unit weight and year of manufacture from the rating plate
Only the trade name of the refrigerant and the unit's serial number
That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP
The weight and capacity of the pipework and the colour code of the casing paint

214

Easy

How do leaks affect systems using flammable refrigerants?


They lower the temperature
They improve efficiency
Have no effect
They cause refrigerant loss, reduced efficiency and a fire hazard

215

Difficult

Why is it important to limit the refrigerant charge in HC systems?


It doesn't matter
It increases capacity
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It lowers the temperature

216

Easy

Why is the cleanliness of heat exchangers in HC systems important?


It doesn’t matter
Causes leaks
It improves heat transfer and reduces energy consumption
It increases the pressure

217

Easy

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Regular checks for leaks and operating parameters
Disabling safety devices
Increasing the refrigerant charge
Lack of servicing

218

Easy

How does the correct selection of components affect a system using a flammable refrigerant?


It lowers the temperature
It increases the amount of refrigerant
It doesn’t matter
It ensures safe and optimal operation and minimises energy losses

219

Easy

Why is it important to use the correct service tools in HC systems?


It doesn’t matter
It ensures operational safety and reduces refrigerant losses
Causes leaks
It increases energy consumption

220

Easy

How does pipe insulation affect the efficiency of systems containing HC?


Causes leaks
It doesn’t matter
It reduces energy losses and improves efficiency
It increases the pressure

221

Difficult

Which safety class applies to R744?


B2L
A1
A3
A2.

222

Difficult

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a two-phase mixture at intermediate pressure
…a subcooled liquid
…saturated vapour at intermediate pressure
…a supercritical fluid

223

Difficult

In R744 transcritical systems, the gas cooler outlet valve controls:


The inlet temperature to the gas cooler
The gas cooler fans
The outlet temperature of the gas cooler
The pressure in the gas cooler

224

Easy

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°C
K
°R
°F

225

Medium

Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?


The owner, installer and service technician of the unit
Only the date of installation and the installer's name
The make and model of the unit
Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs

226

Difficult

Which statement best describes the behaviour of R717 and mineral compressor oil?


An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 mixes very well with the oil, which easily returns to the compressor
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)

227

Difficult

What is the main reason for using K65 copper tubing in some R744 systems?


They can withstand higher pressures
They have good low-temperature performance
They come in a wider range of diameters
They bend easily

228

Difficult

Which statement about installing Schrader valves is correct?


All Schrader cores are suitable for all refrigerants
Schrader valves must not be used in R744 systems
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Hydrocarbons leak through Schrader valves

229

Difficult

Which refrigerant can be detected with phenolphthalein paper?


R744
R1234ze(E)
R1270
R717

230

Difficult

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure lower, subcooling higher
Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure higher, subcooling lower
Discharge pressure higher, subcooling higher

231

Difficult

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It has a distinctive odour that helps locate the leak
It has a higher pressure than pure nitrogen in the same cylinder
It reacts with refrigerant residues, producing a visible colour change
Its small atoms pass easily through leaks and are detected

232

Difficult

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To avoid damaging the compressor with liquid CO₂
To charge R744 more slowly and measure it more accurately
To prevent the drain valve on the receiver from opening
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)

233

Difficult

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Formation of carbonic acid, which damages the system
Reduced cooling capacity
Formation of hydrogen fluoride and hydrofluoric acid
Excessive discharge pressure

234

Difficult

Which system may require manual oil recovery?


R744 cascade system
Supercritical ‘booster’ system using R744
Secondary system using R744
An R717 system

235

Difficult

The pressure of R744 at a saturation temperature of 20 °C is approx.


25 bar g
56 bar g
90 bar g
14 bar g

236

Medium

Who is responsible for keeping the equipment records?


The person responsible for risk assessment.
There is no such obligation.
The operator of the unit or system.
The equipment maintenance technician.

237

Difficult

Which refrigerant is lighter than air?


R717
R1234ze(E)
R1270
R744

238

Difficult

What hazards are associated with a safety group A3 refrigerant?


Lower flammability, lower toxicity
Higher toxicity, no flame propagation
Higher flammability, lower toxicity
Lower toxicity, no flame propagation

239

Difficult

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


3922
0
6
675

240

Difficult

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Lower flammability limit, height of the indoor unit, floor area
Practical limit, height of the indoor unit, floor area
Practical limit, room volume
Lower flammability limit, room volume

241

Difficult

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


Similar
About 6 times larger
About 1.5 times larger
About half

242

Difficult

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…the same as the high-pressure switch setting
…approx. 27.5 bar g
…the same as the relief valve set pressure
…higher than the maximum allowable pressure (PS) of the low-pressure stage

243

Difficult

What is the correct definition of critical temperature?


The temperature at which a substance changes from a gaseous to a solid state
The temperature at which, for certain substances, electrical resistance is zero
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature above which there are no distinct liquid and gaseous phases

244

Difficult

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat as its temperature falls
…rejects heat as its pressure falls
…rejects heat at constant temperature and pressure
…rejects heat during a phase change

245

Difficult

R717 is highly corrosive to:


titanium
copper (and its alloys)
stainless steel
aluminium

246

Difficult

What can be the effect of a relief valve lifting repeatedly?


The valve stays fully open permanently
The valve no longer opens
The valve may not reseat tightly and its set (opening) pressure may decrease
The set pressure increases

247

Medium

Where are oil traps installed on the suction line?


At the inlet to every component of the refrigeration system
Immediately before the compressor suction connection
Before the safety valve on the suction side
At the bottom of vertical suction risers with upward flow

248

Difficult

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = (p₁ × T₂)/T₁
p₂ = T₁/(p₁ × T₂)
p₂ = (p₁ × T₁)/T₂
p₂ = T₂/(p₁ × T₁)

249

Difficult

What is the recommended pre-alarm level for fixed leak detection systems for R717?


5,000 ppm
500,000 ppm
500 ppm
50,000 ppm

250

Difficult

Why are compressors with a separate motor (open type) mostly used in R717 systems?


Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To lower the condensing pressure
To increase the refrigerant charge
Because they are cheaper

251

Difficult

Which type of compressor is most commonly used in large ammonia systems?


Hermetic scroll
Rotary vane compressor
Diaphragm compressor
A reciprocating or screw compressor

252

Difficult

How is the capacity of a piston compressor regulated in NH₃ systems?


By reducing the refrigerant charge
Solely by adjusting the oil volume
By increasing the condensing pressure
By unloading the cylinders or changing the rotational speed

253

Difficult

How is the capacity of a screw compressor most commonly controlled?


By adjusting the oil level
By changing the type of oil
By using a slide valve
By closing the suction valve

254

Difficult

When is two-stage compression used in NH₃ systems?


Only in small systems
At low evaporating temperatures (pressures) and high pressure ratios
Only with water-cooled condensers
At small temperature differences

255

Difficult

What is the advantage of two-stage compression over single-stage compression?


Higher energy consumption
Higher efficiency and lower discharge temperature
Lower efficiency
No need for a separator

256

Difficult

How does an evaporative condenser used in NH₃ systems work?


It transfers heat only to the air
Operates without a fan
It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency

257

Difficult

What is the function of the liquid separator in an NH₃ system?


It prevents liquid from entering the compressor
Increases the discharge temperature
It separates oil from the refrigerant
Regulates the condensing pressure

258

Medium

Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?


Rising liquid level in the receiver and increasing subcooling
Low suction pressure, high superheat and negligible subcooling
Sight glass full of liquid and rising oil level in the crankcase
Rising condensing and suction pressures with no superheat

259

Difficult

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To reduce the condensing temperature
To increase the oil volume

260

Difficult

What is the role of the float switch in NH₃ systems?


It monitors the liquid level in the tank or separator
It controls the fan’s operation
It regulates the condensation temperature
It is used to detect leaks

261

Difficult

What is a thermosyphon in NH₃ systems?


An oil circulation pump
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
A defrosting device
A type of safety valve

262

Difficult

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


Because NH₃ does not mix with most compressor oils
To reduce the pressure
To increase the amount of refrigerant
Because the oil mixes only with water

263

Difficult

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
To increase fan efficiency
Removing moisture from the system
To separate the oil from the refrigerant and return the oil to the compressor

264

Difficult

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A direct-expansion (DX) system
An indirect system
A glycol system
A pumped liquid-recirculation system

265

Difficult

What is the characteristic feature of a flooded evaporator system?


No level control is required
The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour
No separator is used

266

Difficult

What is the main difference between a direct and an indirect system?


In a direct system, there is no evaporator
In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load

267

Medium

Which components of a refrigeration system are potential leak points subject to leak checks?


Hermetic compressors, liquid receivers and liquid separators
Only high-pressure-side components
Only suction-side components
Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices

268

Medium

What pressure is used for the pressure tightness test of an installation?


Always 30 bar
A pressure equal to the maximum pressure measured during operation
A pressure chosen by the technician based on experience
The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS)

269

Medium

At which points of the unit must the leak check be carried out?


At all points where there is a potential risk of refrigerant leakage
Only at connections of measuring instruments
Only on compressor shut-off valves, solenoid valves and filters
Only on discharge-side components

270

Medium

When can a unit be considered tight after a pressure test?


When gas bubbles appear after immersion in water
When the pressure drop does not exceed 0.1 bar regardless of the test duration
When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located
When it has been checked with a fixed electronic detector

271

Medium

Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?


Regulation (EU) No 517/2014
Regulation (EU) 2024/573
Commission Regulation (EC) No 1516/2007
Implementing Regulation (EU) 2024/2215

272

Difficult

Which parts of a refrigeration system should be given particular attention during a leak check?


Compressor and receiver connections, because the pressure is highest there
Only compressor connections, because they are the only parts subject to vibration
Only condenser connections, because the refrigerant is liquid there
Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices

273

Easy

What is the superheat of refrigerant vapour?


The amount of heat required to evaporate a liquid
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The difference between the saturation temperature and the actual liquid temperature in the liquid line
The difference between the condensing temperature and the ambient temperature

274

Difficult

Leak checks can be carried out using various methods. Which pair is correct?


Direct and indirect methods
Material quality control methods and electronic methods
Methods with and without quality control of supplies
Physical and chemical methods

275

Difficult

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


A person who has carried out such checks before
An employee appointed by the owner of the installation
Any leak-testing specialist
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)

276

Difficult

What conditions must be met to use UV dye for leak checking?


A UDT authorisation for pressure testing is required
It is sufficient that introducing dye into the circuit is technically feasible
Manufacturer approval of the method and a certificate covering breaking into the circuit
It is sufficient to have a UV lamp, dye and safety goggles

277

Difficult

Which leak-checking methods are considered direct methods?


Pressure-change measurement and immersion in water
Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions

278

Difficult

What do indirect leak-checking methods involve?


Leak detection with UV dye
Ultrasonic measurement
Leak detection with an electronic detector
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume

279

Medium

How should the pressure be increased during a pressure tightness test?


In one step, by fully opening the nitrogen cylinder valve
Gradually, in stages, checking for leaks at each level until the test pressure is reached
As quickly as possible
In any way

280

Medium

What electronic equipment should be used for leak checking?


Only hot-cathode devices
Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically
Only detectors with an infrared sensor
Only devices with an 'ion pump' sensor

281

Medium

What documentation should be checked before starting a leak check?


The operator's fixed-asset inventory ledger
Only the installation invoice and the first start-up report
The equipment records – especially recurring problems and previous leaks
Attendance sheets of the plant-room staff for the year

282

Medium

What information must be recorded in the leak check report?


Date, number and location of leaks, how they were repaired, technician details and signature
The method used, the time spent on site and the cost of repair
The date, a general note about the leak and the operator's signature
Only the number of leaks found and the date of the check

283

Medium

What pressure should be used for the pressure tightness test?


Any pressure, at the technician's discretion
Always 10–12 bar
A pressure not exceeding the maximum allowable pressure of the system (PS)
Always 2–3 bar

284

Medium

What is the temperature glide of a refrigerant?


The temperature drop of the refrigerant across the expansion valve
In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure
The temperature rise of the vapour in the compressor
A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure

285

Difficult

What does a vacuum (decay) test involve?


The pump runs continuously to hold the required vacuum for the test
The pump is restarted every time the system pressure rises
With the pump running, you watch the vacuum gauge reading
After isolating the pump, you check whether the system pressure rises

286

Difficult

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


At least once every 12 months.
Once every six months.
Only when servicing the unit.
On initial commissioning.

287

Difficult

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Only when servicing the unit.
At least once every 12 months.
Once every six months.
On initial commissioning.

288

Medium

In which equipment is a leakage detection system required?


Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases)
Equipment with 30 kg or more of F-gases, regardless of their GWP
Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type

289

Difficult

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the charge is 100 kg or more of ozone-depleting substances
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the equipment operates in an enclosed space
the equipment contains a flammable refrigerant in any quantity

290

Difficult

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Visual inspection
Measurement with a handheld electronic detector
Leak checking with a fluorescent dye introduced into the circuit
Checking with a foaming solution

291

Medium

What should you check before using a portable electronic leak detector?


That it has an infrared sensor, as only this type is permitted
That it has been zeroed close to the suspected leak point
That it holds a valid UDT inspection certificate
That it suits the refrigerant and has been checked as the manufacturer requires

292

Medium

Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?


All except D
Only E
Only A1 and A2
A1, A2 and E

293

Difficult

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At any time.
At the next periodic inspection.
Between 24 hours and 1 month after the repair.
Immediately after the repair.

294

Difficult

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 12 months
Every month
Every 3 months
Every 6 months

295

Medium

Why is it advisable to subcool the liquid refrigerant?


To allow a condenser with a smaller heat-exchange surface to be used
To ensure that liquid free of vapour bubbles enters the expansion valve
To allow a smaller expansion valve to be used
To lower the evaporating temperature in the evaporator

296

Medium

What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?


Update the equipment records and carry out a leak check (it may be done directly after repair)
Charge an alternative refrigerant, start up and measure the parameters
Visually inspect only the bolted and brazed joints near the repair
Issue the invoice and leave the leak check to the next periodic service

297

Medium

Recovery of fluorinated greenhouse gases means:


The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal.
The reuse of fluorinated greenhouse gases following a basic purification process.
The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases.
The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties.

298

Medium

Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?


The operator
A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit)
The owner of the installation
The administrator of the operator's account in the register

299

Medium

How must recovered refrigerants be stored?


In a disposable (non-refillable) cylinder that held the same refrigerant
In any used refrigerant cylinder, provided it is leak-tight
In a labelled recovery cylinder with a dual valve and a valid inspection
In any pressure vessel that has some form of approval

300

Medium

When should the recovery of fluorinated greenhouse gases be carried out:


Before each leak test of the equipment.
Only prior to the final disposal of equipment.
Before the final disposal of equipment and, where applicable, during its servicing and maintenance.
Always during servicing and maintenance of equipment.

301

Medium

What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?


Add a special contaminant neutraliser
Clean the mixture yourself using a filter-drier
Pass it through a particle filter and reuse it
Hand it over to a specialised, authorised company for reclamation or destruction

302

Medium

What should be done if different refrigerants have been mixed in a storage cylinder?


Add a special refrigerant to the mixture
Pass it through a filter-drier and reuse it
Separate the mixture into its components yourself
Hand the mixture over to an authorised company – as a rule for destruction

303

Medium

How does push-pull refrigerant recovery work?


The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder
Refrigerant is drawn alternately from the suction and discharge sides of the compressor
The recovery unit draws vapour from the system and condenses it in the cylinder
Nitrogen is injected into the system, pushing the refrigerant into the atmosphere

304

Medium

What are the options for managing waste refrigerant?


Reclamation, recovery
Disposal, storage
Recovery, disposal
Recycling, reclamation, destruction

305

Medium

Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?


Recycling
Storage
Reclamation
Destruction

306

Medium

The lower the evaporating temperature, …


…the lower the density of the suction vapour and the greater the cooling capacity of the compressor
…the lower the density of the suction vapour and the lower the refrigerant mass flow rate
…the greater the density of the suction vapour and the lower the refrigerant mass flow rate
…the greater the density of the suction vapour and the greater the refrigerant mass flow rate

307

Medium

How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?


Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks
Only with weight and capacity marks
The marking is optional
With the manufacturer's logo and date of manufacture

308

Medium

The recovery of refrigerants does not require the use of:


Hoses with shut-off valves.
A refrigerant recovery station.
An electronic leak detector.
Scales with a measurement range suitable for the size of the cylinder being filled.

309

Medium

What functions does the compressor perform in a refrigeration system?


The compressor compresses ambient air and increases the pressure of the refrigerant.
The compressor creates a vacuum on the suction side of the system
The compressor condenses the refrigerant.
The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure.

310

Easy

What is the compression ratio of a compressor?


The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of suction pressure to discharge pressure (po/pc)
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The ratio of absolute discharge pressure to absolute suction pressure (pc/po)

311

Medium

What is compressor flooding (liquid slugging)?


Excess oil in the condenser
Liquid refrigerant or oil entering the compression chamber
A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition
Flooding of the compressor by rainwater

312

Medium

Within what range is the compressor motor speed typically controlled using a frequency inverter?


Speed control does not change the cooling capacity
Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer)
By a maximum of 10%
From approximately 10% to 90% of nominal capacity

313

Easy

What is the theoretical displacement (swept volume flow) of a compressor?


The volume of refrigerant flowing in one piston cycle under actual operating conditions
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)
The volume of a single cylinder in cm³
A value expressed by the coefficient of performance (COP)

314

Medium

Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?


Because these types of compressors are sensitive to voltage drops.
Because this type of compressor has difficulty starting up if the phase sequence is changed.
Because the motor speed would decrease, and consequently the compressor’s capacity.
Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors.

315

Medium

What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?


Less than approximately 8
Greater than 10
Greater than 18
Equal to 1

316

Medium

Why is a shaft seal necessary in open-type compressors?


To prevent air from entering and refrigerant from leaking out of the compressor
To ensure the bearing remains lubricated
Only to prevent oil leakage
To protect the crankshaft bearing

317

Medium

How can you check whether the liquid refrigerant is sufficiently subcooled?


Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure
Check whether the whole evaporator surface is covered with an even layer of frost
Check by touch whether the condenser outlet is noticeably colder than ambient
Check whether the liquid distributor upstream of the evaporator feels warm

318

Medium

Why is the compressor crankcase heated?


To limit refrigerant migration into, and dissolution in, the oil during standstill
To increase dissolution of refrigerant in the oil and improve its viscosity
To keep the lubricating oil liquid
To dehydrate the oil

319

Easy

What is the clearance (dead) volume of a reciprocating compressor?


The volume between the valve plate and the piston crown at top dead centre
The space between the underside of the piston and the crankcase cover
The space between the side of the piston and the cylinder
The volume between the valve plate and the piston at bottom dead centre

320

Medium

What are compressor packs (racks)?


Units with two-stage compressors
Sets of compressors connected in any configuration
Several compressors connected in parallel on a common frame with common suction and discharge headers
Several air-cooled condensers

321

Medium

What is the main advantage of multi-compressor packs?


A smaller refrigerant charge than a single-compressor system
Low purchase cost and easy installation without special controls
Stepwise capacity matching to demand, plus redundancy
No need for compressor controls and safety devices

322

Medium

What is meant by the operating envelope (application range) of a compressor?


A range determined only by the evaporating temperature
The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate
A range determined by the evaporating temperature at a given ambient temperature
The capacity, refrigerant type and dimensions of the compressor

323

Medium

What are the basic functions of oil in a compressor?


Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors)
Increasing the cooling capacity of the refrigerant
Sealing leaks that develop in the installation
Absorbing moisture from the refrigerant

324

Medium

What are the most effective ways of controlling compressor cooling capacity?


Partially covering the evaporator
Changing the displacement: varying the rotational speed or unloading cylinders
Pressure control valves
An expansion valve

325

Medium

What does hot-gas bypass capacity control involve?


Bypass is not used for capacity control
High-pressure liquid is injected into the suction to increase capacity
The compressor speed is varied
Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity

326

Medium

What is the fundamental difference between hermetic and semi-hermetic compressors?


Both can be dismantled; they differ only in cooling capacity
The semi-hermetic casing is bolted (can be opened); the hermetic one is welded
Semi-hermetic compressors run more quietly as a complete unit
The semi-hermetic compressor has no motor inside the casing

327

Medium

How does a scroll compressor work?


It uses two screws to compress the refrigerant.
A scroll compressor is also known as a turbo compressor.
It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll.
It is a type of piston-type device.

328

Medium

What physical process takes place in the evaporator?


The refrigerant is subcooled as a liquid
The refrigerant condenses
The secondary fluid (glycol, water) evaporates while the refrigerant condenses
The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet

329

Medium

What is the purpose of compressor capacity control?


To ensure compressor lubrication
To match the cooling capacity to the current demand
To match capacity to the condensing temperature
To increase the condensing pressure

330

Medium

Why is inverter speed control advantageous for refrigeration compressors?


It enables continuous, smooth control of cooling capacity
Reducing the speed improves oil return to the compressor
It increases compressor capacity above nominal at any frequency
It can be used with any compressor to ensure lubrication

331

Medium

Does the suction gas temperature affect the cooling capacity of the compressor?


Yes – higher temperature lowers vapour density, mass flow and capacity
Yes, but only if the suction gas is deeply cooled
Yes, but only in reciprocating compressors, not scroll
No – capacity depends only on the compressor displacement

332

Medium

In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?


Only screw compressors.
Only scroll compressors.
Yes.
No.

333

Medium

What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?


This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off.
This compressor condenses the refrigerant whilst the vehicle is in motion.
The compressor compresses ambient air and increases the pressure of the refrigerant.
This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running.

334

Medium

Which media most commonly absorb heat from the refrigerant in the condenser?


Air and CO₂
Only a water–glycol mixture
Ammonia
Air or water

335

Medium

What is the function of the condenser in refrigeration systems?


Releasing only the heat from the compressor into the surroundings
Releasing only the heat absorbed in the evaporator into the surroundings
Absorption of heat rejected in the regenerative heat exchanger
Releasing to the environment the heat absorbed in the evaporator and the heat added during compression

336

Medium

If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…


…occurs provided a special condenser is used
…does not depend on temperature
…does not occur
…always occurs regardless of temperature

337

Medium

How is liquid subcooling usually achieved in a refrigeration system?


In the final section of the condenser (or in an additional subcooler)
With hot high-pressure vapour
With an additional heat exchanger using liquid nitrogen
By dissolving the refrigerant in oil

338

Medium

What is the purpose of condenser fan speed control?


To disperse refrigerant in the event of a leak
To keep the condensing pressure at the correct level
Only to protect against exceeding the maximum condensing pressure
To reduce energy efficiency

339

Medium

Which international agreement introduced the global phase-down of HFC production and consumption?


The Kigali Amendment to the Montreal Protocol
The Kyoto Protocol
The Paris Agreement
The Vienna Convention for the Protection of the Ozone Layer

340

Medium

Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?


The Stockholm Convention
The Paris Agreement
The Montreal Protocol
The UN Framework Convention on Climate Change (UNFCCC)

341

Difficult

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR4 for all substances
AR6 for all substances

342

Difficult

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


No checks required (below 3 kg)
At least every 12 months (5.22 t CO₂ eq)
Every 6 months
Every 3 months

343

Difficult

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


When it contains less than 5 t CO₂ eq
Always, regardless of charge
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases
Never – hermetically sealed equipment is always checked

344

Difficult

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – at least every 6 months (every 12 months with a leakage detection system)
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
No – HFOs are not subject to leak checks
Yes – every 12 months, because its GWP is low

345

Difficult

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes – bans apply only to new equipment
Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes, if the equipment has a leakage detection system
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)

346

Difficult

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


No – the ban covers all refrigerants with GWP ≥ 750
Only with reclaimed refrigerant
No – the ban covers all HFCs
Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500

347

Medium

Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?


Yes, always
No – recovered F-gas may be used for filling only after it has been recycled or reclaimed
Yes, if the operator agrees
Yes, if less than 24 hours have passed

348

Medium

Who may purchase HFCs for servicing refrigeration equipment?


Any business
Only a person holding the relevant certificate or an undertaking employing such persons
Any adult
Only the equipment operator

349

Medium

Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?


When evidence is provided that installation will be carried out by a certified undertaking
When the user signs a statement that they will install it themselves
Unconditionally
Only if the unit contains less than 3 kg of refrigerant

350

Medium

By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?


By 12 March 2025
Never – the certificate is valid indefinitely
By 31 December 2030
By 12 March 2029 (and then at least every 7 years)

351

Medium

What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?


Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215)
Apply for an extension without training
Nothing – Category I automatically becomes A1
Update their knowledge to the level of Certificate E

352

Medium

What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?


Recovery of F-gases from equipment <3 kg
Leak checks without breaking into the circuit
All activities in Article 2(1) in relation to ammonia (NH₃)
All activities in relation to CO₂

353

Medium

May a person enrolled in a certification training course carry out certified activities?


Yes – with no time limit, if employed by a certified company
No, never
Yes – independently, for 6 months
Yes – under the supervision of a certified person, for no more than 24 months in total

354

Medium

How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?


At least 1 year
At least 5 years
At least 2 years
Until the equipment is decommissioned

355

Difficult

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes – the ban applies only to units >12 kW
Yes – the ban applies from 2029
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes, if the unit is hermetically sealed

356

Difficult

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2029
From 1 January 2025
From 1 January 2027
From 1 January 2035

357

Difficult

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Trifluoroacetic acid (TFA)
Ozone
Carbon dioxide
Carbonic acid

358

Medium

What distinguishes class 2L refrigerants from class 2?


Higher toxicity
Heat of combustion above 19 MJ/kg
No lower flammability limit
A maximum burning velocity of no more than 10 cm/s

359

Medium

What is the lower flammability limit (LFL) of propane R290?


Approx. 0.307 kg/m³
Approx. 1.8 kg/m³
Approx. 0.038 kg/m³ (approx. 2.1% by volume)
Approx. 0.38 kg/m³

360

Difficult

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


1.2 kg
1.5 kg
13 × LFL ≈ 494 g
150 g

361

Difficult

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 13.8 kg
approx. 1.5 kg
approx. 0.46 kg
approx. 4.6 kg

362

Medium

Equipment marked 'Ex II 3G' may be used in zone:


2 (explosive gas atmosphere unlikely and short-lived)
1
0
20 (dusts)

363

Medium

How is explosion hazard zone 2 defined?


An explosive atmosphere is likely to occur in normal operation
An area where flammable refrigerants are never used
An explosive atmosphere is present continuously or for long periods
An explosive atmosphere is not likely in normal operation and, if it occurs, persists only for a short period

364

Medium

Under which UN number is propane (R290) carried under ADR?


UN 3337
UN 3252
UN 1005
UN 1978

365

Difficult

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


20 kg
Unlimited
333 kg
1000 kg

366

Medium

At what concentration should a portable flammable gas detector used for R290 work raise an alarm at the latest?


At 5% propane by volume
No higher than 25% of LFL
At 100% of LFL
At 150% of LFL

367

Medium

How should a recovery cylinder be prepared before filling it with a hydrocarbon refrigerant?


Purge it with compressed air
No preparation is needed
Partly fill it with nitrogen to 5 bar
Evacuate it (no air) and label it for the specific flammable refrigerant

368

Medium

What is the correct approach in a risk analysis before work on an HC system?


Having a fire extinguisher is sufficient
First eliminate hazard sources (e.g. ignition sources); where this is not possible, identify them and apply mitigating measures (ventilation, detection, PPE)
First select PPE, then possibly remove ignition sources
The risk analysis is done after the work is finished

369

Difficult

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 13 kg
approx. 4.94 kg
approx. 0.99 kg
approx. 0.15 kg

370

Medium

Which property of ammonia helps people detect a leak early?


It is odourless
It is denser than air
A very low odour threshold (a few ppm)
It is yellow in air

371

Medium

What hazard does a large CO₂ leak in an enclosed room pose to people?


Formation of hydrogen fluoride
Explosion of the mixture with air
Accumulation near the floor and asphyxiating/toxic effects at high concentrations
CO₂ is completely safe

372

Difficult

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


Gas cooler pressure drops – extra charge is added
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
CO₂ freezes in the gas cooler – heaters are used
Efficiency does not depend on climate

373

Medium

What is floating head pressure and what does it achieve?


It increases subcooling by flooding the condenser
It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference)
It keeps a constant high condensing pressure all year
It means switching condenser fans off periodically

374

Medium

How do SEER/SCOP differ from EER/COP?


SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511)
EER/COP are always higher than SEER/SCOP
There is no difference – they are synonyms
SEER/SCOP apply only to natural-refrigerant equipment

375

Medium

Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?


Omitting pipe insulation
Adding a second liquid receiver
Larger liquid-line diameters
An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume

376

Medium

Why must the charge of small, critically charged R290 systems be weighed to within a few grams during service?


Because extra R290 improves efficiency
Small charge deviations significantly change superheat/subcooling and efficiency, and overcharge increases the risk in a leak
Because scales are not needed – charging is done by sight glass
Because R290 is more expensive than HFCs

377

Medium

Which information must be entered in the equipment records after a leak check?


Only the operator's signature
The date and result of the check and the identity of the undertaking and person who performed it (with certificate number)
Only the equipment's energy consumption
Only the date of the check

378

Medium

What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?


Carry out a direct-method examination to locate the leak
Record it and check at the next periodic inspection
Nothing – indirect methods are sufficient
Top up the refrigerant and end the check