F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Easy


2

Easy

What is the base unit of mass in the International System of Units (SI)?


N
t
lb (pound)
kg

3

Easy

The refrigerant absorbs heat when…


…it condenses
…it is subcooled
…it freezes
…it evaporates

4

Easy

What does the GWP indicator mean?


Ozone depletion potential
The ability of a substance to restore the ozone layer
Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
The annual rise in mean air temperature caused by the emission of 1 kg of the gas

5

Easy

What is the main function of a safety valve?


Prevents the evaporator from freezing
It monitors the moisture content of the refrigerant
Discharges refrigerant when the set pressure is exceeded
It controls the oil level in the compressor

6

Easy

What is the unit of pressure in the International System of Units (SI)?


bar (gauge)
psi (pound per square inch)
Pa (pascal)
atm (standard atmosphere)

7

Easy

What is the log(p)-h diagram for CO₂ used for?


For analysing thermodynamic processes in a refrigeration system
To detect leaks
To regulate pressure
To measure temperature

8

Easy

What can be read from the log(p)-h graph?


Only the temperature
Only the humidity
Only the amount of refrigerant
Pressure, enthalpy, temperature and state of the refrigerant

9

Easy

What are CO₂ saturation tables used for?


To determine the oil quantity
To determine the relationship between temperature and pressure at saturation
To regulate the compressor
To measure humidity

10

Easy

What does the CO₂ saturation state mean?


Dry ice state
A state of high pressure
Equilibrium between the liquid and vapour phases
A state in which the refrigerant is only a gas

11

Easy

Why is understanding the log(p)-h graph particularly important for CO₂?


It is only used for design purposes
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It doesn’t matter
It only applies to NH₃

12

Easy

Why do CO₂ systems require precise pressure control?


Due to significant pressure changes with temperature fluctuations
They do not require control
Due to low pressures
Because there are no valves

13

Easy

What is the basic requirement when charging a system with R717 (NH₃)?


Charging must only take place at temperatures below 0°C
NH₃ can be charged together with air
Charging can be carried out without personal protective equipment
Charging should take place in a well-ventilated area using appropriate personal protective equipment

14

Easy

What is the correct procedure for recovering R717 from a system?


The gas can be released into the atmosphere
The refrigerant can be drained into the sewer system
Recovery is not required
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃

15

Easy

How should R717 (NH₃) be stored?


In sealed, labelled containers, in a cool and well-ventilated place
In any open containers
In unmarked plastic containers
Near heat sources

16

Easy

What is the main hazard associated with an R717 leak during maintenance work?


Increased cooling efficiency
Damage to electrical equipment only
Toxic to humans and may cause chemical burns
No risk whatsoever

17

Easy

What personal protective equipment is required when working with NH₃?


Only a safety helmet
No requirements
Workwear only
Safety goggles, gloves and respiratory protective equipment

18

Easy

How do system leaks affect compressor energy efficiency?


Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
They improve efficiency because condensing pressure drops
No effect as long as the system still cools
They affect only safety, not energy use

19

Easy

How does a dirty condenser affect the operation of the refrigeration system?


Causes an increase in pressure and energy consumption by the compressor
It has no effect
It lowers the condensing pressure
It improves efficiency

20

Easy

Why is adequate airflow through an air-cooled condenser important?


It ensures effective heat rejection and low condensing pressure
It doesn't matter
The lower the airflow, the lower the condensing pressure
It affects only noise

21

Easy

How does the presence of limescale in a water-cooled condenser affect performance?


It has no effect
It lowers the condensation temperature
Impairs heat exchange and increases energy consumption
It improves heat transfer

22

Easy

How do condenser leaks affect energy efficiency?


They lower the temperature
Causes refrigerant loss and a drop in efficiency
They improve efficiency
Have no effect

23

Easy

How important is the correct positioning of an air-cooled condenser?


It should be housed in a small room
It should be installed in a well-ventilated area with unobstructed airflow
It doesn’t matter
It should be close to heat sources

24

Easy

How does hot air recirculation affect the condenser?


It reduces the pressure
It has no effect
Impairs cooling and increases energy consumption
It improves efficiency

25

Easy

How does evaporator icing affect the system’s operation?


It has no effect
It improves cooling performance
It lowers the condensation temperature
Impairs heat exchange and increases energy consumption

26

Easy

How does dirt on the evaporator surface affect its performance?


It has no effect
Impairs heat exchange and increases energy consumption
It reduces the pressure
It improves efficiency

27

Easy

What maintenance task is crucial for the evaporator?


Increasing the refrigerant charge
Lack of maintenance
Regular cleaning and defrosting
Reduced airflow

28

Easy

How does superheat at the evaporator outlet affect efficiency?


It has no effect
Excessive superheat reduces energy efficiency
It only causes a temperature drop
It always improves performance

29

Easy

How do leaks in the evaporator affect efficiency?


Improves performance
Increase capacity
Have no effect
These cause refrigerant loss and a drop in efficiency

30

Easy

How important is correct expansion valve adjustment?


Ensures optimal evaporator charge and improves efficiency
Causes leaks
It increases energy consumption
It doesn’t matter

31

Easy

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It improves efficiency
It has no effect
It lowers the condensing temperature
It causes cooling losses and increased energy use

32

Easy

How does correct TEV adjustment affect system energy efficiency?


It causes leaks
It ensures optimal superheat and improves efficiency
It increases energy use
It has no effect

33

Easy

What happens if the superheat set by the TEV is too high?


Cooling efficiency will improve
Efficiency will drop because the evaporator is not being fully utilised
The refrigerant charge will increase
It has no effect

34

Easy

How do contaminants in the system affect the operation of the TEV?


They improve its performance
Have no effect
They lower the temperature
They can cause it to become blocked and reduce efficiency

35

Easy

What role does the filter-drier play in terms of system efficiency?


It doesn’t matter
It increases the amount of refrigerant
Removes moisture and contaminants, improving the system’s efficiency
It lowers the temperature

36

Easy

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


It increases energy consumption
It causes leaks
It doesn’t matter
Prevents unwanted heat gains and improves efficiency

37

Easy

How important is it to check the operation of the condensing pressure control valve in the system?


It has no effect
It increases energy consumption
It causes a significant rise in temperature
Ensures operation within the optimum pressure range and reduces energy losses

38

Easy

How does the correct selection of a TEV affect energy efficiency?


It increases the amount of refrigerant
Ensures the system is matched to its capacity and operates optimally
It lowers the temperature
It doesn’t matter

39

Easy

What is the function of high-pressure control valves in CO₂ systems?


They control the pressure on the high-pressure side and optimise system operation
They lower the evaporator temperature
They regulate oil flow
They are used to store the refrigerant

40

Easy

Why do CO₂ systems require more advanced automation than traditional systems?


They do not require automation
Because there are no valves
Due to low pressures
Due to the need for precise control of pressure and temperature

41

Easy

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is not required for hermetically sealed systems
Colour-coding of pipes is sufficient
The labelling must indicate the type of substance and the flammability hazard
Labelling is required only in technical rooms

42

Easy

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


Risk of leakage and the formation of an explosive mixture
Merely a reduction in efficiency
Merely installation difficulties
No impact on safety

43

Easy

How should an employee respond when a gas alarm is triggered?


Carry on working until they see a leak
Reduce the pressure in the system
Switch off the system and wait for the alarm to stop
Leave the room immediately and notify their supervisor

44

Easy

Gas detectors should be installed in rooms where:


The room is less than 5 m²
Any refrigerant is present, regardless of the quantity
The amount of refrigerant exceeds a specified permissible threshold
Ventilation is natural

45

Easy

How do leaks affect systems using flammable refrigerants?


They lower the temperature
Have no effect
They improve efficiency
They cause refrigerant loss, reduced efficiency and a fire hazard

46

Easy

Why is the cleanliness of heat exchangers in HC systems important?


It improves heat transfer and reduces energy consumption
It doesn’t matter
It increases the pressure
Causes leaks

47

Easy

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Disabling safety devices
Increasing the refrigerant charge
Lack of servicing
Regular checks for leaks and operating parameters

48

Easy

How does the correct selection of components affect a system using a flammable refrigerant?


It ensures safe and optimal operation and minimises energy losses
It doesn’t matter
It lowers the temperature
It increases the amount of refrigerant

49

Easy

Why is it important to use the correct service tools in HC systems?


It doesn’t matter
It increases energy consumption
It ensures operational safety and reduces refrigerant losses
Causes leaks

50

Easy

How does pipe insulation affect the efficiency of systems containing HC?


Causes leaks
It increases the pressure
It reduces energy losses and improves efficiency
It doesn’t matter

51

Easy

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°F
°C
°R
K

52

Easy

What is the superheat of refrigerant vapour?


The difference between the condensing temperature and the ambient temperature
The difference between the saturation temperature and the actual liquid temperature in the liquid line
The amount of heat required to evaporate a liquid
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)

53

Easy

What is the compression ratio of a compressor?


The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The ratio of absolute discharge pressure to absolute suction pressure (pc/po)
The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of suction pressure to discharge pressure (po/pc)

54

Easy

What is the theoretical displacement (swept volume flow) of a compressor?


A value expressed by the coefficient of performance (COP)
The volume of a single cylinder in cm³
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)
The volume of refrigerant flowing in one piston cycle under actual operating conditions

55

Easy

What is the clearance (dead) volume of a reciprocating compressor?


The volume between the valve plate and the piston crown at top dead centre
The volume between the valve plate and the piston at bottom dead centre
The space between the underside of the piston and the crankcase cover
The space between the side of the piston and the cylinder