1

Közepes

Why is ammonia (NH₃) considered a toxic refrigerant?


It is highly irritating to the respiratory tract and toxic if inhaled
It is colourless and odourless, so it is difficult to detect
It does not react with water, which makes it difficult to neutralise
It is flammable and can form explosive mixtures with air

2

Nehéz

What is the main difference between a dry evaporator and a flooded evaporator?


A dry evaporator has a lower operating pressure than a flooded one
A dry evaporator does not require an expansion valve, whereas a flooded one does
A dry evaporator is filled with refrigerant liquid, whilst a flooded evaporator is filled with gas
A dry evaporator allows the entire refrigerant to evaporate in the pipe upstream of the compressor; in a flooded evaporator, part of the refrigerant remains in a liquid state within the evaporator

3

Nehéz

What is the typical pressure in deep-freezing systems (below −40 °C) for an evaporator in a system using R717?


A pressure varying between 10 and 20 bar
Atmospheric pressure, approximately 1 bar
Negative pressure (vacuum), below 0 bar
Positive pressure, in the range of 5–10 bar

4

Nehéz

Why are PFAS substances formed as a result of the decomposition of certain F-gases problematic?


They are readily biodegradable, so they only pollute the environment for a short time
They are persistent, accumulate in the environment and may be toxic
They cause rapid cooling of the atmosphere
They are climate-neutral

5

Nehéz

What is the basic requirement when charging a system with R717 (NH₃)?


Charging should take place in a well-ventilated area using appropriate personal protective equipment
Charging can be carried out without personal protective equipment
Charging must only take place at temperatures below 0°C
NH₃ can be charged together with air

6

Nehéz

How should oil be handled in systems using R717?


Oil can be mixed with any refrigerant
The oil does not require any monitoring
The oil should be checked regularly and any excess removed from the lower parts of the units to prevent reduced heat transfer and leaks
Oil has no effect on the system’s operation

7

Nehéz

What is the correct procedure for recovering R717 from a system?


The gas can be released into the atmosphere
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The refrigerant can be drained into the sewer system
Recovery is not required

8

Nehéz

How should R717 (NH₃) be stored?


In sealed, labelled containers, in a cool and well-ventilated place
In any open containers
In unmarked plastic containers
Near heat sources

9

Nehéz

What should be done in the event of R717 contamination?


Release into the atmosphere
Continue to use without restriction
The refrigerant must be purified or sent for disposal in accordance with regulations
Add water to dilute it

10

Nehéz

What is the main hazard associated with an R717 leak during maintenance work?


Damage to electrical equipment only
Toxic to humans and may cause chemical burns
Increased cooling efficiency
No risk whatsoever

11

Nehéz

What action should be taken if an NH₃ leak is detected?


Close your eyes and carry on working
Increase the pressure in the system
Ignore it and carry on working
Evacuate personnel immediately and remove the source of the leak, if it is safe to do so

12

Nehéz

What role do scrubbers play in NH₃ systems?


Neutralises ammonia through absorption in a liquid (e.g. water)
They increase the pressure in the system
They are used to measure temperature
They store the refrigerant

13

Nehéz

How should the system be prepared before filling with R717?


Simply start it up
The pressure must be increased above the standard level
There is no need to check it
Check for leaks, remove air and moisture, and create a vacuum

14

Nehéz

What are the transport requirements for R717?


Transport is not subject to regulations
It can be transported without labelling
It can be transported in open containers
Must be transported in suitable, labelled containers in accordance with ADR regulations

15

Nehéz

What personal protective equipment is required when working with NH₃?


Only a safety helmet
Safety goggles, gloves and respiratory protective equipment
No requirements
Workwear only

16

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with compressor oil, so the oil remains in the system on the high-pressure side as a layer above the R717
R717 does not mix with compressor oil, so the oil remains in the system on the low-pressure side as a layer beneath the R717
R717 mixes very well with compressor oil and easily returns to the compressor
In an R717 system, a return oil line cannot be used because the oil is too hot

17

Nehéz

Which system may require manual oil recovery?


Secondary system using R744
Supercritical ‘booster’ system using R744
An R717 system
R744 cascade system

18

Nehéz

Which refrigerant is lighter than air?


R1270
R717
R744
R1234ze

19

Nehéz

R717 is highly corrosive to


titanium
stainless steel
copper
aluminium

20

Nehéz

What is the effect of repeatedly opening the relief valve?


The valve will not open
The relief pressure rises
The valve remains fully open continuously
The relief pressure drops

21

Nehéz

What is the relationship between the pressure (P) and temperature (T) of nitrogen at the start (1) and end (2) of the leak test?


P2 = T1/(P1 × T2)
P2 = (P1 × T1)/T2
P2 = (P1 × T2)/T1
P2 = T2/(P1 × T1)

22

Nehéz

What is the recommended alarm level for fixed leak detection systems for R717?


5,000 ppm
50,000 ppm
500 ppm
500,000 ppm

23

Nehéz

Why are compressors with a separate electric motor most commonly used in R717 (NH₃) refrigeration systems?


To reduce the condensing pressure
Because compressors with a separate motor are cheaper
Because NH₃ reacts with the motor windings and hermetic compressors are not used
To increase the amount of refrigerant in the system

24

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


A reciprocating or screw compressor
Hermetic scroll
Rotary vane compressor
Diaphragm compressor

25

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


By reducing the refrigerant charge
By increasing the condensing pressure
Solely by adjusting the oil volume
By unloading the cylinders or changing the rotational speed

26

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By changing the type of oil
By closing the suction valve
By using a slide valve
By adjusting the oil level

27

Nehéz

When is two-stage compression used in NH₃ systems?


At very low vapour pressures and high pressure differentials
At small temperature differences
Only with water-cooled condensers
Exclusively in small systems

28

Nehéz

What is the advantage of two-stage compression over single-stage compression?


Lower efficiency
Higher efficiency and lower discharge temperature
No need for a separator
Higher energy consumption

29

Nehéz

How does an evaporative condenser used in NH₃ systems work?


It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency
Operates without a fan
It transfers heat only to the air

30

Nehéz

What is the function of the liquid separator in an NH₃ system?


Regulates the condensing pressure
It prevents liquid from entering the compressor
Increases the discharge temperature
It separates oil from the refrigerant

31

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To increase the oil volume
To reduce the condensing temperature

32

Nehéz

What is the role of the float switch in NH₃ systems?


It regulates the condensation temperature
It is used to detect leaks
It monitors the liquid level in the tank or separator
It controls the fan’s operation

33

Nehéz

What is a thermosiphon in NH₃ systems?


A type of safety valve
An oil circulation system utilising differences in pressure and temperature
A defrosting device
A type of evaporator

34

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


Because the oil mixes only with water
To reduce the pressure
To increase the amount of refrigerant
Because NH₃ does not mix with most compressor oils

35

Nehéz

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
To separate the oil from the refrigerant and return the oil to the compressor
Removing moisture from the system
To increase fan efficiency

36

Nehéz

Which NH₃ system features direct evaporation of the refrigerant in the evaporator?


Indirect system
Glycol system
Thermosiphon system
Direct expansion (DX) system

37

Nehéz

What is the characteristic feature of a flooded evaporator system?


No separator is used
The evaporator is filled exclusively with vapour
The evaporator contains a large amount of liquid, which improves heat transfer
No level control is required

38

Nehéz

What is the main difference between a direct and an indirect system?


In an indirect system, no compressor is used
In an indirect system, NH₃ flows directly into the space being cooled
In a direct system, there is no evaporator
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load